Post by paulvk » Sat, 08 Dec 2018, 17:15
The reason for the relay on the output to put an earth on the neutral when inverter is on
is because you should have only one earth/neutral link
if there is a permanent one on the output of the inverter
in bypass mode you will end up with two
The neutral coming in is disconnected in inverter mode
so it needs to be applied in inverter mode
It also needs to be before the mains differential safety relay not after it
You have an earthing problem
There should be no voltage difference between neutral and earth
You should also check the neutral relay in the inverter is working
brucetheloon
Real Name: Bruce
Post by brucetheloon » Sun, 09 Dec 2018, 17:21
Good day everyone. New member from South Africa here, installed a PIP-5048MS with the 60A solar charger limit (RCT MKS-5000-58 model number on the label) in 2014 with 8 102AH AGM batteries in 4 x 2 array for 48V 204AH, no solar panels yet.
With the resumption of load-shedding in this part of the world, I've been investigating adding solar to the mix and have been poking around my inverter unit a bit. Two things I've noticed that I'm running 52.30 firmware version and that there is no U2 secondary CPU firmware version appearing in the LCD parameters list if you Up/Down through the list. the U1 main one is there and it skips through straight back to the first item on a Down press.
Two questions thus arise, is it normal for the secondary CPU firmware version item to be missing like that or has something happened to the SCC hardware? Secondly, what DSP firmware can I go to, straight to 73.00d or am I restricted to older versions.
Label on the side of the machine.
Ksears
Big problems with PIP4848 - R / S / T (3 Phase) - ZERO PV input
Post by Ksears » Sun, 09 Dec 2018, 18:17
Hi there,
since a few days there is no PV Input into my PIP 4048MS - 0volts and 0watts and 0amps....
my configuration:
3x pip 4048MS 5KVA 0.8PF with 6x 250W panels. (2 in a row )
6x pylontech us2000b plus. = 48V battery string.
for 7-9 months everthing works fine.
Now since two or three days no PV input voltage
things i've checked:
-> Use a Multimeter = up to 70V and 3 to 7 amps input by each string (measured on the pip "PV" Terminals). So i think with the pv panels everything is ok?!
-> Reset every device to factory settings and re entered all the values manual.
Any ideas?
PV input measeared by multimeter 70V and displayed on PIP = 0V why?
Post by coulomb » Mon, 10 Dec 2018, 05:47
Good day everyone.
Welcome.
... , no solar panels yet.
Yes, it's normal to not see the secondary CPU firmware version when you don't have panels connected; the solar charge controller only gets its power from the PV input.
Yes, you can go straight to 73.00d. The only hassle is you will have the option to choose up to 140 A of total charge current, when your hardware isn't capable of it. Just ignore the 130 and 140 A options.
The patched firmware goes to some trouble to work with older SCC firmware, so you won't have to update the SCC firmware.
CrOhN
Post by CrOhN » Mon, 10 Dec 2018, 16:58
Whel, false alarm on my inverter problem. Yesterday i took a more relaxed diagnosis time. Inverter is fine. Problem was with a power supply i use to equalize the batteries. As it is connected directly to output of the inverter (only a power socket), when i disconnected all the circuit-breakers, it would still trip the differential, because the socket direct connection to the inverter. That's what you get when you diagnose things after a day's work and wife buzzing you because of all the disconnects....
What is the latest firmware i can use with my inverter? I'm on the 52.30 and 1.24SCC.
6mdx
Real Name: Robert Black
Post by 6mdx » Tue, 11 Dec 2018, 07:50
paulvk wrote:
Mon, 05 Nov 2018, 05:56
Hello erland82
Remote monitoring is easy to do by using a RS232 to TCPIP HLK RM04 module
no programming knowledge required they are ready built just need a box and 5volts
I use them for my two systems that are 250Km apart so I can monitor both
from either location , settings can also be changed.
Would the temperature get that low where the units would be
they should be installed in fully protected area with good ventilation
they are not sealed against the environment
Batteries have problems at that low temperature.
Looking at your diagram the ML4860 has RS232 the HLK RM-04 has two ports for RS232
so you can monitor both with it.
If you get a HLK RM-04 now you can remotely monitor/control the ML4860 now
Also the HLK RM-04s can connect unit to unit creating RS232 > TCPIP -------- TCPIP > RS232 link
They are also have a wifi access point and router built in.
Hi paulvk, I ordered the HKL RM04, CAN SEE IT ON WIFI, BUT cant access due to password. No info with device re password. Any ideas?
Post by coulomb » Tue, 11 Dec 2018, 07:56
Glad that's sorted.
Same answer as for brucetheloon, you can run 73.00d, or if you're keen to beta test the very latest, 73.00e with KettleKomp™.
Post by weber » Tue, 11 Dec 2018, 10:21
The latest firmware can always be found via the Firmware section of the index, which is in the first post (first page) of this thread.
Post by paulvk » Tue, 11 Dec 2018, 14:05
Here is the manual
https://www.prometec.net/wp-content/upl ... manual.pdf
admin/admin
also home page for router is 192.168.16.100/home.asp
It can be run off the power from PIP RJ8 jack
just needs a small switch mode power supply to get the 5V from the 15V
that is how I run my units
I have no problems changing settings on the PIPs using them
Re: Big problems with PIP4848 - R / S / T (3 Phase) - ZERO PV input
Post by weber » Tue, 11 Dec 2018, 14:20
Hi there,
Any ideas?
Hi Ksears. When you say that you measured, with multimeter, 3 to 7 amps input by each string, are you saying that your pv array is charging your battery via the inverter, but the inverter is merely not displaying the PV voltage, power or current? Or are you instead saying that you can measure short-circuit current from the array but it is not charging your battery via the inverter. Either way, it sounds like a problem with the SCC (Solar Charge Controller) inside your inverter.
Does the PV array icon show up on the LCD when there is sun on the PV array?
arnolde73
Real Name: Ethan Arnold
Post by arnolde73 » Thu, 13 Dec 2018, 22:07
I have my ESP8266 logger running now, logging straight to my webserver (InfluxDB/grafana). When I get it fixed up a little nicer I will post some screenshots (if anyone's interested).
One thing puzzles me: I calculate the pvPower from pvCurrent and pvVoltage, and log+chart that, as well as the SCCpower reading. Today I noticed that the calculated power is (approximately) twice as high as the SCC reading. Any idea why?
(By the way, I've ditched my worn-out AGM batteries *sniff* and hooked up a Pylontech US2000B instead. Already much better, apparently the AGM's have only 10-20% capacity left. I will get at least one more hooked in parallel soon.)
6mdx
Post by 6mdx » Fri, 14 Dec 2018, 04:18
weber wrote:
Wed, 10 Oct 2018, 16:38
Release Version of Patched Firmware 72.20c for some PF1 models with the 64V option
[Edit1: On 12-Oct-2018 we replaced beta 72.20b here, with beta 72.20c that has a new load-control or go-to-standby command.]
[Edit2: On 11-Nov-2018 we replaced beta 72.20c here, with release 72.20c. The only change was the first letter of the version number (from B to L).]
This patched firmware fixes the premature-float bugs in the manufacturer's firmware for the PIP-5048MS, Axpert MKS 5K-48 (PF1 with 64V option) and equivalents. i.e. machines supplied with main firmware version 72.xx where xx ≤ 30. It also contains our Dynamic Current and Load Control (DCLC) and AussieView™ additions, and we have provided a version with our voltage and current threshold changes for LFP cells. i.e. It has the same functionality as 73.00c (PF0.8) except that in the LFP version, the minimum tail current to go from absorb to float has now been reduced from 5 A per machine
Hey guys been running the lpf version since the day of release, thankyou.
Have had no issues, but a question or two.
Regarding absobtion, what time period is desireable?
Regarding charging, I am not getting the charging I expected. I have 4.5kw of panels 3s3p per pair or strings (for total of 18 x 60 cell) but seldom see over 2.5kw going into the battery (have seen 53A charging for an hour two). 02 is set to 80A, and util charging is set to 10A
On another note are you planing to add the kettle mod to this release?
Cheers Robert.
Post by coulomb » Fri, 14 Dec 2018, 06:43
PV power is pvCurrent multiplied by battery voltage, not PV voltage. The reported "PV current" is battery-side current, not PV-side current as most users expect.
Post by weber » Fri, 14 Dec 2018, 09:39
Cheers Robert.
Hi Robert. Thanks for letting us know that the LFP version of 72.20c is working for you.
Regarding absorb time. I think that with LFP cells it is best to use the "Aut" setting. This will go to float when the battery voltage is within 0.5 V of the absorb setting and the charge current (in whole amps) falls below either 3 amps or setting [02] divided by 12, whichever is greater. So in your case it would go to float when it fell below 6 amps, i.e. when it dropped to 5 amps (for 30 seconds).
Regarding your low charging current: What size is your battery, what make and model of cells, and what is your absorb voltage setting? I'm wondering if your absorb voltage is too low to overcome the battery internal resistance at more than 53 amps. There is a small chance that this could instead be due to a bug in our patched firmware 72.20c. This could be determined by reflashing with the original 72.20 and seeing if that particular problem goes away. But I think we would have heard from others by now if that was the case.
Yes, we are planning to put out a beta 72.20d as soon as possible, which will have the KettleKomp mod for the PIP-5048MS. The irony is, we originally wrote KettleKomp for the PIP-5048MS, back when Tom kindly loaned us his 5048s for testing. But in early testing, we loaded some bad code that meant the bootstrap loader never got called again, and so we could never load any more code—commonly referred to as "bricking it".
I immediately ordered a replacement control board from MPPSolar. That was on the 23rd of October. The ordering process was a nightmare. Sending photos of the board we wanted, and the serial number of the inverter, eventually sorted it out (or so we thought). Then there were problems with their online payment system. Tom was more than patient, but when, after 4 weeks, I queried the status of the order, and learned that they still hadn't shipped it, I ordered a whole new inverter to be delivered to Tom, on eBay (at least that works). So now I own a 5048MS. The control board finally arrived 4 days ago (after 7 weeks!), but the nightmare isn't over. The new board arrived with unfamiliar firmware (version 71.20) which is missing the equalisation settings, and the board has some different resistors and capacitors. So there have been more emails back and forth with MPPSolar, sending photos of the new and old boards and the inverter label. I'm still waiting for them to tell me what the story is. Maybe it's the wrong board, or maybe it just needs a firmware update.
6mdx
Post by 6mdx » Fri, 14 Dec 2018, 16:12
Runing aut
Battery is 15s 180 aH CALB
Asorbtion setting is 52.5 V
Excellent
I immediately ordered a replacement control board ...
Bummer
So frustrating
Post by weber » Fri, 14 Dec 2018, 16:40
That's plenty of absorb voltage for that battery, so the limited charge current is a mystery to me.
6mdx
Post by 6mdx » Fri, 14 Dec 2018, 17:16
Weber thanks for the info and answers.
Ok well rather than reflash I have a new 5048ms waiting to be setup. So i will hook it up to the battery and panels tomorrow and check the charge current. Big issue will be waiting for sun.
erland82
Real Name: Erland
Post by erland82 » Sat, 15 Dec 2018, 03:51
Got my 5048MS last week, but it was slightly damaged in shipping.
https://imgur.com/a/5yhkboF
https://imgur.com/a/Ys43kn6
I have talked to Mpp, and they are waiting for a reply from DHL.
I haven't been able to test it yet, waiting for a 48v psu before I drag it up to the mountains.
https://imgur.com/DqfCoIT
Here is my PIP-heatbox, it is almost complete.
[ Edited Coulomb: fixed imgur images. @erland82 , please see this post. ]
Tesla Model X100D 2017
Nissan Qashqai+2 4wd 2013
Mazda 323 GTX 4wd 1990
6mdx
Post by 6mdx » Sat, 15 Dec 2018, 09:01
Weber, I swapped the inverters over. The original factor firmware, instantly produced more than 10 amps extra charge (43A vs 33 A) than the 72.20c in the other inverter. Have seen peak currenr around 76A from the factory version. Yet never seen over 53 A from 72.20c
Go figure.
More to think about
Cheers Robert
arnolde73
Post by arnolde73 » Sat, 15 Dec 2018, 22:55
Multiplying battery voltage with solar panel current is about as much good as multiplying the weather with a stock index... they have little to do with each other. The incoming solar power is the PV string voltage times string current, that goes into the MPPT logic (or better: The MPPT adjusts the current so as to maximize I*U) and the battery gets battVoltage*battCurrent to charge, which should be PV_Power minus load and inverter losses (heat).
If my solar string (280W panels 3S4P) is delivering 125V at 8A (1000W) the battery is getting i.e. 20A at 50V = 1000W (minus maybe 50W losses, with no load). So if pvPower (SCC) is pvCurrent * battVoltage, that would be 8A*50V=400W which is complete bullshit. Are you sure thats the case?
Or did you mean, the SCC pvPower is battVoltage*battCurrent(both as coming from SCC)? Then at least that reading would make sense.
Post by coulomb » Sun, 16 Dec 2018, 06:15
Yes, obviously I didn't make myself clear. The so-called "PV input current for battery" or "PV input current 1" [ edit: was "PV current" ] reported by the inverter is actually the SCC output current. [ Edit: I unhelpfully said "In later manuals, this is changed to "MPPT charging current", which is a little clearer.", but that's misleading. The LCD always showed net battery current, i.e. charge source current minus battery load curent. ] It's possible that the PIP MPPT algorithm tries to maximise output current, instead of the usual panel power, so they don't bother measuring panel current at all.
[ Edit: panel current -> panel power. ]
[ Edit: more corrections interspersed, sigh. ]
daimyo
Real Name: Teo
Post by daimyo » Wed, 19 Dec 2018, 05:57
Hi everybody,
I finally get to login... have learned a lot from this forum... GREAT thanks to everybody and especially site Admins.
I am from Croatia and I have 3 PIP MS4840 in parallel, and 21 250W solar panels.
Currently I am on 72.70 FW and it works great for now. Thinking to upgrade to 73.00e.
Hope that I may help someone someday as You have helped me.
Sorry for bad english and best regards. ;)
Post by coulomb » Wed, 19 Dec 2018, 06:22
Hi everybody,
Welcome.
If your question is whether this is possible, the answer is yes. Any genuine Voltronic Power inverter running 72.70 can enjoy the benefits of 73.00d (latest release) or 73.00e (beta). 73.00e has been in beta for a while now with no reports of problems, so it will likely be declared to be the latest release version soon. Edit: but to run them in parallel, they'll all have to be updated.
daimyo
Real Name: Teo
Post by daimyo » Wed, 19 Dec 2018, 06:34
So maybe the best way is to wait some more time and then to install 73.00e FW?
Do I need to turn OFF other two inverters when doing FW upgrade on one?
Post by coulomb » Wed, 19 Dec 2018, 06:47
I've moved two posts about inverters with 450 V MPPTs to a new topic, PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC). This topic is getting too long to talk about every possible model variant. (Edit: I've moved a few more over; there are 23 posts in that topic as I write.)