which power specification is correct?
- Adverse Effects
- Senior Member
- Posts: 1172
- Joined: Sat, 01 Jan 2011, 03:30
- Real Name: Adverse Effects
- Location: Brisbane
which power specification is correct?
the Specs say
2.5HP
6kW
15Amps
that cant work can it?
2.5HP = ~1.86kW / 240VAC = ~7.7677Amps
6kW /240VAC = 25Amps
15Amps * 240VAC = 3.6kW
Window Wall Cooling Only Air Conditioner 6kW
2.5HP
6kW
15Amps
that cant work can it?
2.5HP = ~1.86kW / 240VAC = ~7.7677Amps
6kW /240VAC = 25Amps
15Amps * 240VAC = 3.6kW
Window Wall Cooling Only Air Conditioner 6kW
If you don't have time to do it right,
When will you have time to do it over
Help those who help themselves first
When will you have time to do it over
Help those who help themselves first
-
- Senior Member
- Posts: 3183
- Joined: Mon, 26 Nov 2007, 05:39
- Real Name: Matthew Lacey
- Location: Perth, WA
Re: which power specification is correct?
No power factor correction would be my guess. Also hp wouldnt include fans
Matt
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
- Adverse Effects
- Senior Member
- Posts: 1172
- Joined: Sat, 01 Jan 2011, 03:30
- Real Name: Adverse Effects
- Location: Brisbane
Re: which power specification is correct?
my point was
how can a 6kW airco have 2.5HP and only draw 15 amps
when
2.5HP = ~1.86kW / 240VAC = ~7.7677Amps
6kW /240VAC = 25Amps
15Amps * 240VAC = 3.6kW
none of those amounts come close to matching
how can a 6kW airco have 2.5HP and only draw 15 amps
when
2.5HP = ~1.86kW / 240VAC = ~7.7677Amps
6kW /240VAC = 25Amps
15Amps * 240VAC = 3.6kW
none of those amounts come close to matching
If you don't have time to do it right,
When will you have time to do it over
Help those who help themselves first
When will you have time to do it over
Help those who help themselves first
- jonescg
- Senior Member
- Posts: 4718
- Joined: Thu, 21 Jan 2010, 23:05
- Real Name: Chris Jones
- Location: Perth, WA.
- Contact:
Re: which power specification is correct?
Sometimes they refer to the 'cooling power' or the rate of heat removal. That would be closer to 1.8 kW I'd think.
AEVA National President, WA branch director.
-
- Senior Member
- Posts: 1952
- Joined: Thu, 30 Sep 2010, 20:11
- Real Name: Terry Covill
- Location: Mannum SA
Re: which power specification is correct?
Cooling/heating kW is not necessarily electrical energy used, the EER or COP comes into play. The current rating is to allow for a stalled compressor so it doesn't trip the circuit breaker every time it cycles back in as the compressor usually stops on a compression stroke.
Soft start air con units bleed off the head pressure and start the fans up before the compressor to stagger the load, inverter technology starts the compressor at a very slow spin after the fans are up to speed so a very soft start. The part that catches a lot of people is that inverter technology air conditioners do ramp up to full load plus a bit until they pull the temp down and only then do they reduce the compressor speed to match the load required. Not unusual to see an inverter technology unit ramp up to a 4kW electrical load for 20 mins after start up before it drops back to as little as a 1.2kW electrical load and then back to maybe 750w if the insulation is good.
T1 Terry
Soft start air con units bleed off the head pressure and start the fans up before the compressor to stagger the load, inverter technology starts the compressor at a very slow spin after the fans are up to speed so a very soft start. The part that catches a lot of people is that inverter technology air conditioners do ramp up to full load plus a bit until they pull the temp down and only then do they reduce the compressor speed to match the load required. Not unusual to see an inverter technology unit ramp up to a 4kW electrical load for 20 mins after start up before it drops back to as little as a 1.2kW electrical load and then back to maybe 750w if the insulation is good.
T1 Terry
Green but want to learn
- brendon_m
- Senior Member
- Posts: 1315
- Joined: Sat, 28 Oct 2017, 11:00
- Real Name: Brendon McCarrol
- Location: Perth, Western Australia
Re: which power specification is correct?
This is it, its equivalent to a 6kw bar heater, it's just 200ish% efficient because it's taking energy from the air outside (or inside when cooling) as well as the power lines.
- Adverse Effects
- Senior Member
- Posts: 1172
- Joined: Sat, 01 Jan 2011, 03:30
- Real Name: Adverse Effects
- Location: Brisbane
Re: which power specification is correct?
so its a overunity device
takes ~7.7677Amps from the wall (~7.7677Amps * 240VAC = 2.5HP) then outputs 6kW of cooling from the said ~7.7677Amps
so that is a ~322% increase in power over what is put in it from the wall
and so on that math you should be able to string them together and make positive power out put (i know this cant happen but the numbers dont lie LOL )
PS:-no i am not an overunity nutcase
takes ~7.7677Amps from the wall (~7.7677Amps * 240VAC = 2.5HP) then outputs 6kW of cooling from the said ~7.7677Amps
so that is a ~322% increase in power over what is put in it from the wall
and so on that math you should be able to string them together and make positive power out put (i know this cant happen but the numbers dont lie LOL )
PS:-no i am not an overunity nutcase
If you don't have time to do it right,
When will you have time to do it over
Help those who help themselves first
When will you have time to do it over
Help those who help themselves first
- brendon_m
- Senior Member
- Posts: 1315
- Joined: Sat, 28 Oct 2017, 11:00
- Real Name: Brendon McCarrol
- Location: Perth, Western Australia
Re: which power specification is correct?
It's free energy!
Big oil has been keeping it under wraps for years.
Big oil has been keeping it under wraps for years.
- Johny
- Senior Member
- Posts: 3749
- Joined: Mon, 23 Jun 2008, 16:26
- Real Name: John Wright
- Location: Melbourne
- Contact:
Re: which power specification is correct?
Not quite but is is true that for the same electrical power input, a heat exchanger provides almost twice the cooling power and about 150% more heat than a purely resistive heater.
The heat pump hot water salesfolk call it "heat from the air" or similar.
- brendon_m
- Senior Member
- Posts: 1315
- Joined: Sat, 28 Oct 2017, 11:00
- Real Name: Brendon McCarrol
- Location: Perth, Western Australia
Re: which power specification is correct?
I think you missed the sarcasm.
However it is technically free energy, you're taking heat energy from the air which power companies haven't worked out how to charge us for (yet), so it's energy for free.
However it is technically free energy, you're taking heat energy from the air which power companies haven't worked out how to charge us for (yet), so it's energy for free.
- Johny
- Senior Member
- Posts: 3749
- Joined: Mon, 23 Jun 2008, 16:26
- Real Name: John Wright
- Location: Melbourne
- Contact:
Re: which power specification is correct?
Sorry Brendon, I should have read more closely who posted that remark. I know from your previous posts that you wouldn't have been serious. The over-unity debate got pretty hot here a couple of years ago.
- brendon_m
- Senior Member
- Posts: 1315
- Joined: Sat, 28 Oct 2017, 11:00
- Real Name: Brendon McCarrol
- Location: Perth, Western Australia
Re: which power specification is correct?
No worries, I know tone and meaning is lost in text.
- Adverse Effects
- Senior Member
- Posts: 1172
- Joined: Sat, 01 Jan 2011, 03:30
- Real Name: Adverse Effects
- Location: Brisbane
Re: which power specification is correct?
ROFL
If you don't have time to do it right,
When will you have time to do it over
Help those who help themselves first
When will you have time to do it over
Help those who help themselves first
- Richo
- Senior Member
- Posts: 3737
- Joined: Mon, 16 Jun 2008, 00:19
- Real Name: Richard
- Location: Perth, WA
Re: which power specification is correct?
Yes global warming IS free!
Remember it's only free until you get caught
We are currently on the buy it now and pay for it later plan
And that balloon payment is fast approaching
So the short answer is NO but the long answer is YES.
Help prevent road rage - get outta my way!
Help prevent road rage - get outta my way!
- woody
- Senior Member
- Posts: 1716
- Joined: Sat, 21 Jun 2008, 02:03
- Real Name: Anthony Wood
- Location: Mt Colah
Re: which power specification is correct?
Better late than never - this is my understanding...
Cooling:
~6kW of heat comes out of the intake air
~2kW comes from electricity
~8kW of heat goes into the outside air
----
0kW sum
Heating:
~7kW of heat goes into the air coming out of the blower
~2kW of that comes from electricity
~5kW of that comes from outside air
----
0kW sum
Current Rating Amps 15A = shouldn't blow the fuse on a 15A circuit - it may go over that momentarily and will be under it by a long way mostly.
Cooling:
~6kW of heat comes out of the intake air
~2kW comes from electricity
~8kW of heat goes into the outside air
----
0kW sum
Heating:
~7kW of heat goes into the air coming out of the blower
~2kW of that comes from electricity
~5kW of that comes from outside air
----
0kW sum
Current Rating Amps 15A = shouldn't blow the fuse on a 15A circuit - it may go over that momentarily and will be under it by a long way mostly.