Hi,
I've been running a pip4048ms with 240Ah of batterys (4s2p Ritah AGM 120Ah) now for 13months. I've just notice in the last week that the solar volts soon after sunrise climbs above the 115vdc which the manual indicates PV Array MPPT Voltage Range 60~115Vdc . During this approx 2hr period there is no battery charging and I can hear a relay clicking every few seconds in the pip.
I've attached a couple of graphs.
solrv.png
batta.png
I have resolved this on 1 occasion by shutting down the pip and restarting other times it has come good after a couple of hrs.
Can anyone offer any clues on why the pip isn't charging the battery on some blue sky mornings?
I have emailed mpp solar with no reply at this stage.
Regards
Al.
**Update
Same issue again this morning. Blue sky, relay clicking in pip, Battery not charging.
Steps taken
1. Turned off solar. Pip relay still clicking
2. Turned off pip.
2. wait a couple of minutes then turned on pip. After a short time ( a minute maybe ) pip would shutdown.
3. turn pip off then wait a bit then turn on. This time switched on solar. Pip relay clicking.
repeat some combination of the above steps a few times without success.
4. Fired up genny. At least I have power and batterys are charging. Genny overload trips and pip switches to battery providing power but still no solar charging and pip relay still clicking.
I turn off genny. At this stage have to leave so I leave everything as is hoping it will sort itself out.
On my return I check and see that about 8:30am (same as previous morning) the pip behaves as normal with solar charging.
I'm hopeful someone can shed some light on whats causing this. My next step is to check all battery connections.
Regards
Al.
***Update
I'm thinking now its just the time of the year and angle of sun on panels in the morning.