Tesla PW2

Post by Rusdy »

Damn this guy called Elon Musk. He hit my weak spot. I have this unhealthy addiction to anything battery powered and inverters. When one combined them both, then who am I to resist? Need to remortgage the house for this, hence, my family will live on boiled water and salt from now on (powered by PW2)!

Wheel added so it can fit to a 'vehicle' forum:
Image

My observation to date, can be found here.

Too bad Tesla took the wording out of the older advertisement: "Powerwall provides backup power during utility outages, natural disasters and even the Zombie Apocalypse (you know it's coming).". Since it's pretty much what it is at the current cost.
mikedufty
Senior Member
Posts: 805
Joined: Tue, 02 Dec 2008, 00:15
Real Name: Michael Dufty
Location: Perth, Western Australia
Contact:

Re: Tesla PW2

Post by mikedufty »

Is the anti islanding, backup function when the grid goes down built in, or something that had to be installed specifically? Couldn't find much detail of that in their webpage previously.

Roughly how much did it cost installed?
Rusdy
Groupie
Posts: 320
Joined: Mon, 09 Jun 2014, 16:45
Real Name: Rusdy
Location: Australia
Contact:

Re: Tesla PW2

Post by Rusdy »

The battery and the 5kW inverter is definitely built-in to the same enclosure (with the big a$$ Tesla logo on it). The 'Gateway' box, from what the installer told me (and also from Tesla's block diagram) contains a 'switch'. I'm guessing this is a remote controlled switch (controlled by the PW2) as an anti-islanding switch. During installation, I did see a big ass circuit breaker on the 'gateway' box. The gateway box is ugly as.

So that we're on the same page, the gateway box is a separate enclosure and must be installed close to the electricity meter / DB:
Image

It cost me AUD12,100. However, my PW2 is quite a distance from the gateway box (roughly 15 metres). Also, I got charged extra since my house is 3-phase (4 CTs to monitor 3 phases and solar input).
Rusdy
Groupie
Posts: 320
Joined: Mon, 09 Jun 2014, 16:45
Real Name: Rusdy
Location: Australia
Contact:

Re: Tesla PW2

Post by Rusdy »

For those who have PW2, and found the new TBC (Time Base Control) is confusing, I did a wee bit different experiments and concluded that TBC Cost Saving with peak time extension to cover the shoulder is not a bad idea (in order to reduce solar exports, for those with poor FiT).

I also found a quirk that stop the PW2 charging from the grid during off-peak. More details here.
reecho
Senior Member
Posts: 940
Joined: Sun, 17 Apr 2011, 02:39
Real Name: Richard
Location: Perth WA
Contact:

Re: Tesla PW2

Post by reecho »

Interesting info from a Tesla owner on his new PW2 install..

https://youtu.be/c9jpLItCJws
User avatar
Adverse Effects
Senior Member
Posts: 1171
Joined: Sat, 01 Jan 2011, 03:30
Real Name: Adverse Effects
Location: Brisbane

Re: Tesla PW2

Post by Adverse Effects »

reecho wrote: Sat, 09 Jun 2018, 20:06 Interesting info from a Tesla owner on his new PW2 install..

https://youtu.be/c9jpLItCJws
you beat me to it been watching him for a year or 2 lol

he lives a not to far from me
If you don't have time to do it right,
When will you have time to do it over

Help those who help themselves first
Chad
Noobie
Posts: 2
Joined: Fri, 01 Jun 2018, 19:44
Real Name: Chad

Re: Tesla PW2

Post by Chad »

Adverse Effects wrote: Sat, 09 Jun 2018, 21:06
reecho wrote: Sat, 09 Jun 2018, 20:06 Interesting info from a Tesla owner on his new PW2 install..

https://youtu.be/c9jpLItCJws
you beat me to it been watching him for a year or 2 lol

he lives a not to far from me
Interesting.. Obviously a very savvy guy.
One question springs to mind though.. (2 actually !) ..
1)..With all the impressive data capture and display (how many monitors :shock: ).. Why did he need to hack together a separate LCD etc to show the PW capacity level ?
2)..And , what was the readout on that LCD showing ? ...84.??? What ? Cetainly not kWh (or does he have 7+ PW units ?)
But anyway,.. i thought there was a phone App that gave realtime PW data remotely ?
adam lippiatt
Noobie
Posts: 23
Joined: Wed, 25 Feb 2015, 20:10
Real Name: Adam Lippiatt
Location: Perth

Re: Tesla PW2

Post by adam lippiatt »

Hi

Does anyone have current pricing in Perth for the Powerwall 2? Any installer that can be recommended?

I have a quote from over east company but I am starting to worry about the install as they told me that western power is no longer allowing the install of powerwall 2s on single phase properties with any solar already installed.

I got in touch with Western Power and they confirmed it is a 5kVA grid tied inverter limit that is in place. Affects people who already have solar adding a battery and using a hybrid inverter plus their existing grid tied inverter. Not powerwalls.

That they couldn’t tell the difference worries me.

Thanks

Adam
T1 Terry
Senior Member
Posts: 1948
Joined: Thu, 30 Sep 2010, 20:11
Real Name: Terry Covill
Location: Mannum SA

Re: Tesla PW2

Post by T1 Terry »

Doesn't the Powerwall have a hybrid inverter built in to it? Do you already have grid tie solar?

T1 Terry
Green but want to learn
User avatar
jonescg
Senior Member
Posts: 4702
Joined: Thu, 21 Jan 2010, 23:05
Real Name: Chris Jones
Location: Perth, WA.
Contact:

Re: Tesla PW2

Post by jonescg »

It's an AC coupled system, so it comes with an inverter built in. Easiest option for retrofits to grid-tied solar.
AEVA National President, returning WA branch chair.
T1 Terry
Senior Member
Posts: 1948
Joined: Thu, 30 Sep 2010, 20:11
Real Name: Terry Covill
Location: Mannum SA

Re: Tesla PW2

Post by T1 Terry »

So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook :lol:

T1 Terry
Green but want to learn
reecho
Senior Member
Posts: 940
Joined: Sun, 17 Apr 2011, 02:39
Real Name: Richard
Location: Perth WA
Contact:

Re: Tesla PW2

Post by reecho »

T1 Terry wrote: Thu, 29 Aug 2019, 15:18 So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook :lol:

T1 Terry
No...Original grid tie can stay as is.
antiscab
Senior Member
Posts: 3178
Joined: Mon, 26 Nov 2007, 05:39
Real Name: Matthew Lacey
Location: Perth, WA

Re: Tesla PW2

Post by antiscab »

reecho wrote: No...Original grid tie can stay as is.
Especially if you install it without telling Western Power :lol:

best of luck with the bureaucracy
Matt
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
francisco.shi
Senior Member
Posts: 826
Joined: Mon, 17 Sep 2018, 16:30
Real Name: Francisco
Location: Brisbane, Strathpine

Re: Tesla PW2

Post by francisco.shi »

Or you could install enough backup and panels to run off grid and tell western power that you are moving and do not want the connection anymore.
It seems it is becoming easier to go off grid. It is just a matter of how much you get for your excess electricity vs how much you pay in connection fees.
whimpurinter
Senior Member
Posts: 513
Joined: Tue, 05 Jul 2011, 16:32
Location: Brisbane

Re: Tesla PW2

Post by whimpurinter »

Just on the idea of going off grid completely.

I have taken notice of those times where you have heavy cloud cover for days on end, or sun showing on and off all day.
Being off grid would be great until you get that scenario. You'd have to accept that possibility and just wing it for as long as it takes for good old sunshine to kick in again. You couldn't live in a household where not everyone understood the significance of being off the grid.

Living in parts of Australia which really do have lots of sunshine and unfortunately a minimum of rain would be a bonus, to this extent.

As the weather becomes more and more unpredictable and we get cloudy days instead of fine or rain, it is a factor.
Dan007a
Groupie
Posts: 112
Joined: Thu, 08 Nov 2018, 21:04
Real Name: Daniel Andrews

Re: Tesla PW2

Post by Dan007a »

Have played with the idea of using excess sunny days to run a water pump to fill a number of water tanks.and then release water to run water wheels for base loads on cloudy days. 200 wet days year.
User avatar
jonescg
Senior Member
Posts: 4702
Joined: Thu, 21 Jan 2010, 23:05
Real Name: Chris Jones
Location: Perth, WA.
Contact:

Re: Tesla PW2

Post by jonescg »

For times like this, a small petrol generator would suffice. It's prudent to have a plan C anyway.
AEVA National President, returning WA branch chair.
User avatar
jonescg
Senior Member
Posts: 4702
Joined: Thu, 21 Jan 2010, 23:05
Real Name: Chris Jones
Location: Perth, WA.
Contact:

Re: Tesla PW2

Post by jonescg »

Dan007a wrote: Fri, 30 Aug 2019, 08:10 Have played with the idea of using excess sunny days to run a water pump to fill a number of water tanks.and then release water to run water wheels for base loads on cloudy days. 200 wet days year.
For about 11 years, my folks lived in the bush east of Warwick where we had a solid 400 m of elevation behind the house. The top of the ridge wasn't our land, so it was moot, but as an exercise I worked out how much water, head, pipe and power was needed for a small scale pumped hydro scheme. I think I concluded I'd need about 100,000 litres on top of the hill, and a minimum of 25 kW of daytime solar pumping power to supply 12 hours of 3 kW of base load power. I don't think UPVC was able to restrain that much pressure, but would have been a fun (albeit expensive) exercise.

Assuming 1 litre per second flow and 400 m of head, that's 3.5 kW of power on tap. So for 24 hours you would need to release 86400 litres.
AEVA National President, returning WA branch chair.
Dan007a
Groupie
Posts: 112
Joined: Thu, 08 Nov 2018, 21:04
Real Name: Daniel Andrews

Re: Tesla PW2

Post by Dan007a »

Throw in 4 ram pumps as well for fun
T1 Terry
Senior Member
Posts: 1948
Joined: Thu, 30 Sep 2010, 20:11
Real Name: Terry Covill
Location: Mannum SA

Re: Tesla PW2

Post by T1 Terry »

The bother in law does have a mix of solar and hydro to charge his house battery. It is a very old Telecom lead acid battery so it doesn't hold capacity well, so must be recharged daily. He lives on the side of the Huon Valley in Tasmania, about as far south as most would live full time and Tassie is known for its generous rain fall and cloud cover.
His hydro uses a Pelton Wheel, just needs a good flow rather than high pressure, he has 2 permanent springs that feed his supply dam but there is no reason why a constant supply from something like this https://www.ebay.com.au/itm/DC-24V-284W ... 2749.l2649 couldn't be powered from a combo of solar and wind. There is the potential to add as many supply jets as required to get the required torque and jet size to get the required speed while balancing that against water use.
Not quite the idea solution for an urban house off grid system, but great for a country property with a suitable hill near the house.
Green but want to learn
francisco.shi
Senior Member
Posts: 826
Joined: Mon, 17 Sep 2018, 16:30
Real Name: Francisco
Location: Brisbane, Strathpine

Re: Tesla PW2

Post by francisco.shi »

Plan C would be to have two electric cars with 40kwh+ battery each and when supply is too low run off the car battery. When car is getting low you can go to a fast charger and recharge.
If you use say 12kwh/day your car batteries would keep you going for about a week.
adam lippiatt
Noobie
Posts: 23
Joined: Wed, 25 Feb 2015, 20:10
Real Name: Adam Lippiatt
Location: Perth

Re: Tesla PW2

Post by adam lippiatt »

reecho wrote: Thu, 29 Aug 2019, 18:44
T1 Terry wrote: Thu, 29 Aug 2019, 15:18 So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook :lol:

T1 Terry

No...Original grid tie can stay as is.
Yes, the original grid tied inverter stays as is.

The issue is when you install a hybrid inverter with an existing grid tied inverter. Western Power will count both for their 5kVA limit, even if you just propose using the battery inverter component.

In any event, installing a Powerwall which only has a battery inverter does not add towards the five kVA limit.

The downside is the power wall is the more expensive option (at least initially).
T1 Terry
Senior Member
Posts: 1948
Joined: Thu, 30 Sep 2010, 20:11
Real Name: Terry Covill
Location: Mannum SA

Re: Tesla PW2

Post by T1 Terry »

francisco.shi wrote: Sat, 31 Aug 2019, 12:13 Plan C would be to have two electric cars with 40kwh+ battery each and when supply is too low run off the car battery. When car is getting low you can go to a fast charger and recharge.
If you use say 12kwh/day your car batteries would keep you going for about a week.
Then you need the inverter that can handle the electric vehicle battery voltage.
That raises an interesting thought. The inverter I'm looking at to use on a proposed off grid system has a solar feed in voltage max of 450vdc and between 120vdc and 430vdc the MPPT controller part can handle. If the electric vehicle battery was between these 2 figures, 120vdc and 430vdc, could the EV battery be connected to the solar input of the inverter to act as a supply?

T1 Terry
Green but want to learn
antiscab
Senior Member
Posts: 3178
Joined: Mon, 26 Nov 2007, 05:39
Real Name: Matthew Lacey
Location: Perth, WA

Re: Tesla PW2

Post by antiscab »

T1 Terry wrote: Sat, 31 Aug 2019, 14:58
Then you need the inverter that can handle the electric vehicle battery voltage.
That raises an interesting thought. The inverter I'm looking at to use on a proposed off grid system has a solar feed in voltage max of 450vdc and between 120vdc and 430vdc the MPPT controller part can handle. If the electric vehicle battery was between these 2 figures, 120vdc and 430vdc, could the EV battery be connected to the solar input of the inverter to act as a supply?
Yes that works (I do that for capacity testing large packs)
The inverter will run at full power though until you either disconnect it, or the voltage goes outside it's operating window
Matt
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
francisco.shi
Senior Member
Posts: 826
Joined: Mon, 17 Sep 2018, 16:30
Real Name: Francisco
Location: Brisbane, Strathpine

Re: Tesla PW2

Post by francisco.shi »

I have been thinking about how to do this. As you said most solar panel strings would be able to feed the car battery directly. And most solar inverters I assume would have a 400 or so volt bus. So it may be as simple as just connecting the car battery to the internal bus and reprogramming the inverter.
This could potentially fix the duck curve produced by solar without having to spend money in storage. As we get more electric cars they can be used as domestic energy storage.