PIP-4048MS inverter

Post by solamahn » Wed, 01 Jul 2015, 11:32

Chris,
It's got to be a typing error but even so you have nothing to worry about. You will never get more than 60A battery charging out of the solar panels and you will never get more than 60A battery charging from the generator. The generator starts at 5pm so there wont be much solar charging at that time so your combined solar/generator battery charging could never be much more than 60A either. Your size battery bank will tolerate 60A charging. Program 16 could be set to cue but I would set it to SNU. Have 01 UTI and 02 60A or 70A if you cant enter 60A. You might want to have 11 set to something less than 60A so you dont overload the generator. This would depend on the size of the generator and loading by other users. I would set 26 to 56.8 and 27 to 54.5. I just tested a 250Ah battery bank on 60A utility charge, 11 set to 60A and worked fine.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Wed, 01 Jul 2015, 11:39

Thanks for all the help. Tomorrow if I can get the battery cabling sorted out will be the moment of truth.

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Wed, 01 Jul 2015, 12:05

Use big short battery cables. I am installing a 3248ms today. 12 x 280w 36v 4 x 3 and 8 x 250Ah AGM. No utility or generator. 6 panels facing east and 6 facing west. This setup does not seem to upset the MPPT. You might want to have your panels facing more to the east because the generator starts in the late afternoon when the sun is to the west.
Solamahn PNG

User avatar
coulomb
Site Admin
Posts: 3638
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Wed, 01 Jul 2015, 14:10

Scott wrote: I wrote a little calculator app (Windows only): CrcGen

Neat! Thanks for that.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, PIP-4048MS inverter, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Wed, 01 Jul 2015, 23:10

coulomb wrote:
Scott wrote: I wrote a little calculator app (Windows only): CrcGen

Neat! Thanks for that.


I have copied it too. Thanks

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 04 Jul 2015, 18:10

How did you go.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Mon, 06 Jul 2015, 17:35

I have run into a small problem trying to communicate with the PIP using Tera Term. I have Win 8 installed. It will not allow we to setup a serial connection and Win 8 does not seem to have COM ports anymore.

Secondly how does one update the firmware?

I have finished mounting the 12 panels and done the running of conduit and portion of the rewiring that needs to be done (Bringing 2 phases from the generator into the house - 1 phase for general lights and 2nd phase to the PIP and the PIP's output to a few essential lights and plugs). Had a venomous snake in the loft whilst we were rewiring but fortunately she is slugglish and moved off into the deeper recesses of the loft.

Took delivery of 300 sheep ewes on Thursday so no work on the system Thursday or Friday - busy tagging and sorting the new ewes.

Today finish the battery box and wiring - hopefully.

User avatar
coulomb
Site Admin
Posts: 3638
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Mon, 06 Jul 2015, 21:23

ChrisHobson wrote: I have run into a small problem trying to communicate with the PIP using Tera Term. I have Win 8 installed. It will not allow we to setup a serial connection and Win 8 does not seem to have COM ports anymore.
Oh, it does, but some of the older USB to serial adapters don't have Windows 7/8 drivers readily available. I think Weber found some, but I can't find the email now.
Secondly how does one update the firmware?
I've never done it, but I believe everything you need [ edit: software wise ] is provided, and you "just" need to follow the instructions; see this post:
viewtopic.php?title=pip4048ms-inverter& ... 332#p54127

I'm pretty sure you'll need your USB to serial dongle talking properly for this to have any chance of working. Make sure your PIP is of the right age for this firmware update to apply; I believe that there is usually a manufacture date somewhere. Sorry, I have to dash now.
Last edited by coulomb on Mon, 06 Jul 2015, 11:24, edited 1 time in total.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, PIP-4048MS inverter, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

PlanB
Senior Member
Posts: 465
Joined: Sat, 16 Jan 2010, 15:24
Real Name: Kris McLean
Location: Freemans reach
Contact:

PIP-4048MS inverter

Post by PlanB » Mon, 06 Jul 2015, 21:39

The sad state of affairs with USB drivers & a nice fix

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Thu, 09 Jul 2015, 11:54

Hi I finally got the South African PIP to run this afternoon. I could not get the fans to come on but have not connected up the circuits with heavy appliances on them.My wife's hair-dryer (1200W) did not cause the fans to switch on. I am waiting for a DC CB before connecting the PVs. I initially had it running in UPS mode but running on a generator it did not like this an so I reverted to appliance mode.

The problems I was envisaging was fortunately a typo and one can restrict the charging right down to 10 A.

Thank-you all for your help Solarmahn,Coulomb, Weber, Kurt and Scottie (I think).

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Thu, 09 Jul 2015, 12:30

With 52 30 firmware, the fans run much slower on light loads. 1200w should make the fans run. You need to look at them to see them spinning. I turn the fans upside down and apply lanolin grease to their soldered terminals. I notice on late model pips that the fan soldered terminals are now coated so the lanolin grease is probably no longer necessary but I still apply it anyway.
You should use 4 10A DC breakers.
I would leave 02 set at 60A but maybe limit 11 so as not to overload the generator.
Installed another 3248 on Tuesday and doing a 4048 today.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Fri, 10 Jul 2015, 00:39

I was only when I switched the PC off last night that I found that the fans were indeed running, but that they are quieter than the PC. Started this morning at 51V.

I have 4x12A solar fuses. Plan to use the DC CB as an isolator if needed. I am really battling to get some components and cannot get an isolator switch big enough. It seems every South African who can afford it is installing solar due to our government's crap power supply.

How does one check what firmware one is using? My PIP was built in June so I presume it has the latest firmware.

User avatar
coulomb
Site Admin
Posts: 3638
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Fri, 10 Jul 2015, 02:05

ChrisHobson wrote: How does one check what firmware one is using?

It's in the lower left quadrant of the Watchpower software. "Main CPU version" is the *firmware* version for the main processor; "Secondary CPU version" is the firmware version for the SCC (Solar Charge Controller). They are different CPUs, and I believe you update the software for them separately.

You could probably also use the QVFW and QVFW2 commands with all the mucking about with CRCs. The details are on a fairly recent post here.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, PIP-4048MS inverter, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Fri, 10 Jul 2015, 02:08

Or just get it from the LCD screen. Yours is probably 52 30.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Fri, 10 Jul 2015, 10:21

Firmware 72 40. Probably some regional differences.

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Fri, 10 Jul 2015, 11:45

Yes. Thats the lastest version. Be good to know what the difference is between the 2. I will load 72.40 and see if I can notice any changes. One difference between 52 25 and 52 30 is the fan speed. What about U2, the scc firmware. What version have you got for that. You would have to expect that 72 40 is better than 52 30. I had a problem with 52 30 when connecting generators. It would worh with 25 but not with 30. I suspect that the test that the inverter applies to the utility/generator feed is more stringent in 30. I tried apl, ups, different voltage and frequency and everything else I could think of but could not get the inverter to switch to the generator. Mains indicator icon just keeps blinking.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Fri, 10 Jul 2015, 23:28

My secondary CPU says "00000.00". I had trouble with the inverter continually switching between AC and batteries whilst running in UPS but is running smoothly in appliance mode.

Will connect the PVs tomorrow and that might be why secondary CPU has not got a value.

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 11 Jul 2015, 01:30

Yes. The scc is powered from solar power
Solamahn PNG

Tjadenw
Noobie
Posts: 16
Joined: Sat, 11 Jul 2015, 00:43
Real Name: Werner
Location: Cape Town
Contact:

PIP-4048MS inverter

Post by Tjadenw » Sat, 11 Jul 2015, 01:57

Hi

I've read the PIP-4048 forum back to back and learned alot. Im also a south African that's going solar due to our Unstable Grid.

I've got the Aexpert MKS plus 3k and on my model there's no serial port, its only got a USB port so im not sure how to connect to the inverter using terra term. The Axpert MKS Plus is the PIP2424 with the 60 Amp charge controller I guess.

My model also have the fans spinning at max speed all the time so i replaced with Arctic F8 ball bearing fans.


solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 11 Jul 2015, 02:04

You have the latest model. They have changed from rj45 and nine pin cable to usb because most laptops do not have the nine pin serial port
Solamahn PNG

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 11 Jul 2015, 02:11

Here that model is pip2424msx. 60A mppt scc. Model 2448ms is good too. As long as you don't need more than 2.4kw out. They use less idle power. 3000w scc. But no parallel function. What configuration did you use to connect the panels. I use 4 x 2 on the 2424msx. 36v 280w panels.
Solamahn PNG

Tjadenw
Noobie
Posts: 16
Joined: Sat, 11 Jul 2015, 00:43
Real Name: Werner
Location: Cape Town
Contact:

PIP-4048MS inverter

Post by Tjadenw » Sat, 11 Jul 2015, 02:41

One of the reasons I got the 2.4 KW model is the low standby consumption.

I'm still building my setup so only have 2 panels.

Currently I have 2 255W 36v panels in series this will be expanded to 3X2 or 3x3 if the 24 volt model can handle it I think it should be fine.

Getting 340 watt at about 13:00 in the afternoon witch is good for winter I think , pretty close to the Renesola Virtus 255w STC ratings of 189Watt per panel. The Batteries are 4 X 100Ah sealed FLA.

Initially I got the inverter to power all my light circuits and one wall plug circuit that runs my fridge, computers and other light loads during "Loadshedding" wile charging from the grid. Loadshedding is when power gets cut on a rotational bases to certain arias due to energy generation shortages of the country's sole energy suppler.

I then decided to add solar to take parts of my energy consumption off grid, inverter now running in solar priority mode and solar only charge mode.

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 11 Jul 2015, 03:01

2 x 4 works good so 3 x 3 should be ok. It seems like it is better to have the mppt scc fed with higher voltage. The mppt range for 2424msx is 30 - 115. I have tried 1 x 7 and 2 x 8. With 1 x 7, a lot of the time, the PV voltage is around 30 which is too low. 2 x 4 gives PV around 60 when loaded and works good. I will try 3 x 3 sometime. The scc is very robust. I have never had one fail. It should be able to handle 9 x 280w. I have run 3 x 5 on a 2448ms without problem. I would like to try 3 x 3 facing east and another 3 x 3 facing west on a 2448. Most of my jobs have no grid or generator connection so I like to connect lots of panels and batteries.
Solamahn PNG

solamahn
Groupie
Posts: 121
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

PIP-4048MS inverter

Post by solamahn » Sat, 11 Jul 2015, 11:45

Another good setup would be having a 4048ms with 04 set to sen and beside it a 2448ms. Common battery bank. 24 x 280w panels, 3 x 4 to each inverter and have separate ac out feeds. The 2448ms would feed lights, fridge and anything else that is on often and the 4048ms would feed the high power seldom used appliances. Only 20 or so watts idle consumption.
Solamahn PNG

ChrisHobson
Noobie
Posts: 18
Joined: Sat, 27 Jun 2015, 12:04
Real Name: Chris Hobson
Location: South Africa

PIP-4048MS inverter

Post by ChrisHobson » Mon, 13 Jul 2015, 07:31

solamahn wrote: What about U2, the scc firmware. What version have you got for that.


The U2 firmware is 1.24. Connected the panels today but overcast. 104 VDC but no current flowing - tomorrow we will see looks like it is clearing.