Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

Hi,

I have 3xPIP-4048MS with 5400W PV and I am adding 5500W more...

Does anyone know is it possible to "return" excess power, when batteries are full, to grid (power company) with PIPs or I have to buy new 10kW grid inverter to do that?

All suggestions are welcome :)

Thank You.

User avatar
coulomb
Site Admin
Posts: 3885
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by coulomb »

daimyo wrote:
Wed, 05 Feb 2020, 18:21
Does anyone know is it possible to "return" excess power, when batteries are full, to grid (power company) with PIPs or I have to buy new 10kW grid inverter to do that?
My understanding is that the models that can operate without a battery (so that excludes yours) can in some modes push power from PV to AC-out, but I suspect that they aim not to export anything.

So that's a no, unfortunately.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

daimyo
Noobie
Posts: 24
Joined: Wed, 19 Dec 2018, 05:29
Real Name: Teo
Location: Croatia

Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

coulomb wrote:
Wed, 05 Feb 2020, 18:33
daimyo wrote:
Wed, 05 Feb 2020, 18:21
Does anyone know is it possible to "return" excess power, when batteries are full, to grid (power company) with PIPs or I have to buy new 10kW grid inverter to do that?
My understanding is that the models that can operate without a battery (so that excludes yours) can in some modes push power from PV to AC-out, but I suspect that they aim not to export anything.

So that's a no, unfortunately.
OK, Thank You for info.

grfarrow
Noobie
Posts: 6
Joined: Fri, 12 Apr 2019, 15:40
Real Name: Gareth Farrow

Re: PIP-4048MS and PIP-5048MS inverters

Post by grfarrow »

Hey all,

I have an option to go with a 64V inverter which I'd like as my current 5kw with 74.30 does not support patched firmware as yet, but based on the clipping issue at lower voltages I know this is not ideal.

Which is better, the 64V with patched firmware or the unpatched version I have now? If a patch will come out at some point I'd rather wait with my non 64V.

Thanks in advance,

Gareth

User avatar
coulomb
Site Admin
Posts: 3885
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by coulomb »

grfarrow wrote:
Thu, 06 Feb 2020, 15:12
If a patch will come out at some point I'd rather wait with my non 64V.
Patched firmware 74.40e is now in early alpha testing (eyeballing the code). Depending on my time, it should be available for beta testing in the next week or so.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

grfarrow
Noobie
Posts: 6
Joined: Fri, 12 Apr 2019, 15:40
Real Name: Gareth Farrow

Re: PIP-4048MS and PIP-5048MS inverters

Post by grfarrow »

coulomb wrote:
Thu, 06 Feb 2020, 17:57
grfarrow wrote:
Thu, 06 Feb 2020, 15:12
If a patch will come out at some point I'd rather wait with my non 64V.
Patched firmware 74.40e is now in early alpha testing (eyeballing the code). Depending on my time, it should be available for beta testing in the next week or so.
That's amazing news, thank you. Crazy that our purchase decisions are made by enthusiasts that fix factory issues... You guys are rock stars.

solamahn
Groupie
Posts: 135
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

Re: PIP-4048MS and PIP-5048MS inverters

Post by solamahn »

4048V can export to grid
Solamahn PNG
24x300w, 2x4048ms, 75kw AGM
24x280w, JFY6000
12x300w, 4048ms, 20kw Winston
30x280w, 2x4048V, 35kw Winston

User avatar
weber
Site Admin
Posts: 2686
Joined: Fri, 23 Jan 2009, 17:27
Real Name: Dave Keenan
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by weber »

Moderator note:
Moved a repair-related discussion of SCCs to the repair topic:
viewtopic.php?p=77504#p77504
Please continue that discussion in the new topic.
One of the fathers of MeXy the electric MX-5, along with Coulomb and Newton (Jeff Owen).

mojo
Noobie
Posts: 3
Joined: Fri, 31 Jan 2020, 05:34
Real Name: Mo

Re: PIP-4048MS and PIP-5048MS inverters

Post by mojo »

weber wrote:
Fri, 31 Jan 2020, 07:37
@mojo Please post photos of the labels on the sides of the two inverters. Block out the rightmost 6 digits of the serial numbers if you wish.

Hi, sorry for the late reply, was away for a week at the time. Here are the labels, your knowledgeable advice will be appreciated.
new inverter
new inverter
label2.jpeg (68.54 KiB) Viewed 686 times
older inverter
older inverter
label1.jpeg (62.43 KiB) Viewed 686 times

User avatar
coulomb
Site Admin
Posts: 3885
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by coulomb »

Ah. One is a ...5P64 and the other is a ...5P. That means a different turns ratio for the transformer, and a different range for all the battery voltage related parameters. So the CAN packets will be different and incompatible. It will not be possible to parallel them.

It looks like your ...5P64 was bought recently, as it was manufactured in September 2019. Would it be possible to return it for a SOL-I-AX-5P (without the 64 at the end)? I think that the suppliers and/or the manufacturer see the 64 V models as superseding the 58.4 V models, but really they're just a different set of compromises. Sadly, it's possible that even if your supplier is willing to do the swap (perhaps with a generous payment to cover shipping), because of this superseding mentality it might be difficult for your supplier (presumably Mecer) to obtain a non-64 V model.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

daimyo
Noobie
Posts: 24
Joined: Wed, 19 Dec 2018, 05:29
Real Name: Teo
Location: Croatia

Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

solamahn wrote:
Sat, 08 Feb 2020, 13:41
4048V can export to grid
Hi,

Could it be connected in parallel with my 3 existing 4048MS?

I did not find 4048V model on ebay? Do you have some link to it?

Could You please give some more info?

Do you know if 5048MK can export to grid?

Thank You and best regards

T

User avatar
coulomb
Site Admin
Posts: 3885
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by coulomb »

daimyo wrote:
Mon, 10 Feb 2020, 15:18
Could it be connected in parallel with my 3 existing 4048MS?
No.
I did not find 4048V model on ebay? Do you have some link to it?
https://www.mppsolar.com/v3/hybrid-v-series/

The V series are hybrids, not off-grid models, so it's no surprise that they can export to the grid. [ Edit: However, they look more like the off-grid models, and may be based on off-grid hardware. That's speculation on my part. ]
Do you know if 5048MK can export to grid?
The MK (Axpert King) is a 145 V MPPT max model, meaning that it can't export to the grid. It's also the only dual conversion model, and it appears that the converter between the AC-in and battery is never run in reverse. It quite possibly is designed to be unable to do this. It's not clear whether it's possible to operate the inverter proper when the unit is in bypass mode (note: on this model, bypass mode and line mode are very different). In bypass mode, AC-in is connected to AC-out, and the inverter output is connected to AC-out (and hence to AC-in). If such operation is possible, then there would be a path for energy to flow from the PV-in to AC-in, i.e. to the grid. However, none of the operating modes in the manual show this happening.

Actual PIP-5048MK owners may be able to add real-world experience to my theory.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

jdavies1994
Noobie
Posts: 6
Joined: Sat, 16 Feb 2019, 20:19

Re: PIP-4048MS and PIP-5048MS inverters

Post by jdavies1994 »

Hello all it's been a little while since I posted last hope you've all been well. I'm just curious if any of you have used the ICC APM software to switch on a control relay wired into the inverter switch (at the bottom) that switches on/off the slave inverters. And will switch more back on based on power demands etc in the house all programmed through apm.

Can any of you foresee any issues?

Cheers.

rinaldoparaipan
Noobie
Posts: 22
Joined: Mon, 26 Oct 2015, 03:26
Real Name: Dan Paraipan
Location: Romania
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by rinaldoparaipan »

The 100th inverter installed.


Thanks to your help I could manage some problems occurred.(Error 90, fan problems, firmware compatibility, etc, etc.)
You can see my works here:

www.ecowindsolar.ro
Attachments
Panouri fotovoltaice Constanta (1).jpg
Panouri fotovoltaice Constanta (1).jpg (85.04 KiB) Viewed 552 times

daimyo
Noobie
Posts: 24
Joined: Wed, 19 Dec 2018, 05:29
Real Name: Teo
Location: Croatia

Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

coulomb wrote:
Mon, 10 Feb 2020, 17:23
daimyo wrote:
Mon, 10 Feb 2020, 15:18
Could it be connected in parallel with my 3 existing 4048MS?
No.
I did not find 4048V model on ebay? Do you have some link to it?
https://www.mppsolar.com/v3/hybrid-v-series/

The V series are hybrids, not off-grid models...
Thank You... things are now much more clearer. :)

[ Edited Coulomb: trimmed quote ]

daimyo
Noobie
Posts: 24
Joined: Wed, 19 Dec 2018, 05:29
Real Name: Teo
Location: Croatia

Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

coulomb wrote:
Mon, 10 Feb 2020, 17:23
I did not find 4048V model on ebay? Do you have some link to it?
https://www.mppsolar.com/v3/hybrid-v-series/
Ebay seller said that V2 model is EOL and new model is:

https://www.ebay.com/itm/163192198388

User avatar
coulomb
Site Admin
Posts: 3885
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by coulomb »

daimyo wrote:
Thu, 13 Feb 2020, 14:00
Ebay seller said that V2 model is EOL and new model is:
https://www.ebay.com/itm/163192198388
? But the one shown in the Ebay advertisement is a V2. Perhaps he/you meant that the V are now at end-of-life, and the V2 are replacing them. But the V2 are 450 V max MPPT models, so you'd need to add insulation monitoring to be legal in Australia.

I have no idea about the regulations in Croatia. Being a grid-tie capable inverter, they could well require type approval as well; they do in Australia.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

daimyo
Noobie
Posts: 24
Joined: Wed, 19 Dec 2018, 05:29
Real Name: Teo
Location: Croatia

Re: PIP-4048MS and PIP-5048MS inverters

Post by daimyo »

coulomb wrote:
Thu, 13 Feb 2020, 19:22
daimyo wrote:
Thu, 13 Feb 2020, 14:00
Ebay seller said that V2 model is EOL and new model is:
https://www.ebay.com/itm/163192198388
? But the one shown in the Ebay advertisement is a V2. Perhaps he/you meant that the V are now at end-of-life, and the V2 are replacing them. But the V2 are 450 V max MPPT models, so you'd need to add insulation monitoring to be legal in Australia.

I have no idea about the regulations in Croatia. Being a grid-tie capable inverter, they could well require type approval as well; they do in Australia.
My bad... V is EOL, not V2. :roll:

Yes I have asked them again and the seller said that they have CE certificate and do not have EU regional certificates so they do not import it into the EU. :x

mojo
Noobie
Posts: 3
Joined: Fri, 31 Jan 2020, 05:34
Real Name: Mo

Re: PIP-4048MS and PIP-5048MS inverters

Post by mojo »

coulomb wrote:
Sun, 09 Feb 2020, 18:57
Ah. One is a ...5P64 and the other is a ...5P. That means a different turns ratio for the transformer, and a different range for all the battery voltage related parameters. So the CAN packets will be different and incompatible. It will not be possible to parallel them.

It looks like your ...5P64 was bought recently, as it was manufactured in September 2019. Would it be possible to return it for a SOL-I-AX-5P (without the 64 at the end)? I think that the suppliers and/or the manufacturer see the 64 V models as superseding the 58.4 V models, but really they're just a different set of compromises. Sadly, it's possible that even if your supplier is willing to do the swap (perhaps with a generous payment to cover shipping), because of this superseding mentality it might be difficult for your supplier (presumably Mecer) to obtain a non-64 V model.
Thanks for that. Will have to see what is possible.

solamahn
Groupie
Posts: 135
Joined: Thu, 18 Jun 2015, 00:09
Real Name: Julian Leach
Location: PNG

Re: PIP-4048MS and PIP-5048MS inverters

Post by solamahn »

Nice numbers 4048ms
Attachments
image.jpg
image.jpg (2.03 MiB) Viewed 312 times
image.jpg
image.jpg (1.57 MiB) Viewed 312 times
image.jpg
image.jpg (2.07 MiB) Viewed 312 times
image.jpg
image.jpg (2.05 MiB) Viewed 312 times
image.jpg
image.jpg (1.98 MiB) Viewed 312 times
image.jpg
image.jpg (2.04 MiB) Viewed 312 times
Solamahn PNG
24x300w, 2x4048ms, 75kw AGM
24x280w, JFY6000
12x300w, 4048ms, 20kw Winston
30x280w, 2x4048V, 35kw Winston

McMajan
Noobie
Posts: 5
Joined: Thu, 21 Nov 2019, 06:11
Real Name: Stefano Smania

Re: Bricked or not bricked...this is the question....

Post by McMajan »

coulomb wrote:
Sat, 23 Nov 2019, 08:11
All opto-couplers seem to deteriorate slightly with age, so if it was marginal then, it could well be unable to handle a firmware update now. Ordinary communications (commands and responses other than firmware updates) operate at 2400 bps, where there is four times the time for the opto-coupler output to settle at the correct level.
[/quote]
Hi friends.
Yesterday I replaced the opto-couplers of communication board as suggested by Coulomb and yes, now it works fine.

User avatar
weber
Site Admin
Posts: 2686
Joined: Fri, 23 Jan 2009, 17:27
Real Name: Dave Keenan
Location: Brisbane
Contact:

Re: PIP-4048MS and PIP-5048MS inverters

Post by weber »

Awesome remote diagnostic work, @coulomb!
One of the fathers of MeXy the electric MX-5, along with Coulomb and Newton (Jeff Owen).