Search found 29 matches

by ojeysky
Mon, 10 Feb 2020, 03:33
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048MK inverter
Replies: 222
Views: 20348

Re: PIP-5048MK inverter

ive been using https://diytechandrepairs.nu/raspberry-solar/ for logging from my 5048 Mk in 2019... on the display i can read out, daily, monthly, yearly and total usage/production - does any1 now of a similar to above project that will save and present these figures in a database? I use solpiplog ...
by ojeysky
Sun, 26 Jan 2020, 02:18
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Please I have an emergency, I am getting a error 32 communication failure!!!! I am off-grid and really need this to come back on! Please check ethernet cable between controller card and mppt side.also wire between display panel and controller card. I checked all those and they are all fine. If the ...
by ojeysky
Sat, 25 Jan 2020, 20:54
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Please I have an emergency, I am getting a error 32 communication failure!!!! I am off-grid and really need this to come back on!
by ojeysky
Fri, 24 Jan 2020, 09:02
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Attached is my current settings, I like to know if this is okay or whether I should change some of the settings to something else. Your new settings (the top ones with 27.6 and 26.9 V) are what I would recommend, except that I'd change the equalisation period to 1-3 days (see what seems to charge y...
by ojeysky
Fri, 24 Jan 2020, 05:27
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hi, first time posting, i have a PIP5048GK, i have been reading through the forums trying to grasp as much i can understand. Still not sure how to setup the inverter with the best config and would like your help. PIP5048GK inverter is recent model (04 2019) I have checked that its not a clone. I ha...
by ojeysky
Thu, 23 Jan 2020, 22:36
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hello, I got a 24v 5.4kwh (25.6v nominal) LFP. I am trying to figure out a charging algorithm on the GK series since there is no settings for lithium on the CC. Attached is my current settings, I like to know if this is okay or whether I should change some of the settings to something else. Thanks E...
by ojeysky
Tue, 14 Jan 2020, 21:38
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

The strange part is that I did the test when there wasn't significant sunlight... It was around 4pm. So I was surprised to be getting 9.7 and 11A. Oh, 4pm. You might have mentioned that in the original post. I don't think you can complain about 6.7 A @ 4pm. But then, like you, I'm quite surprised a...
by ojeysky
Tue, 14 Jan 2020, 13:46
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

- 2 panels read below spec 6.7A Is this short circuit current in full sunlight? Measured at about the same time (i.e. with the same sun strength) as the ones producing 9.7 A and higher? Yes I did them the same period, like moving from one panel to the other within few seconds. The strange part is t...
by ojeysky
Tue, 14 Jan 2020, 03:56
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

I am no expert here but from what I read, the total output of string is limited by the panel with the lowest current, so in your case it would be the panel with 6.7amp. Sorry for the confusion it's actually 5A that has been my max harvest in the last one month (I have updated my initial post accord...
by ojeysky
Tue, 14 Jan 2020, 03:19
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

I am wondering if this affect the performance of the inverter? i.e does the harvest reduce as the temperature increases? I haven't read the firmware for these models as thoroughly as for the MK series, but it looks like no, the PV current does not appear to derate with temperature. There is no sepa...
by ojeysky
Mon, 13 Jan 2020, 03:34
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP 3024GK Error 09
Replies: 5
Views: 362

Re: PIP 3024GK Error 09

Hello,

I am using this exact model and the temperature goes as high as 45degree, now I am worried seeing your post. The manual indicate operating temperature to be up to 55degree. I am not yet up to 14 months of usage hence would like to hear suggestion on how to prevent this issue.
by ojeysky
Mon, 13 Jan 2020, 03:20
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hello, my GK series inverter operates between 35 and 50C and I am wondering if this affect the performance of the inverter? i.e does the harvest reduce as the temperature increases?
by ojeysky
Tue, 31 Dec 2019, 04:03
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Those PV current readings are so confusing. They could be panel-side or battery-side, and they could be total or net into the battery. Yes indeed, though I have an external monitoring system so that makes it easier for me to know which is which. I am attaching the highest I could get today from a 2...
by ojeysky
Mon, 30 Dec 2019, 13:51
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

My question is whether this is normal behaviour with 3024 GK series; does more batteries mean lesser amperage generation? Are you referring to current on the PV side, or on the battery side? Am referring to the current on the PV side, before I added new panels I used to get up to 8A!see attachment)...
by ojeysky
Sun, 29 Dec 2019, 21:10
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hello folks, I am trying to get my head around this; I have noticed that since I added 2 more panels and got 4 new batteries my instantaneous hervest in amps has never gotten above 5amps. However when I was using 6 Panels with 2 batteries, there was a day I got 8.2amps. Today I decided to test the 2...
by ojeysky
Thu, 10 Oct 2019, 18:55
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048MK inverter
Replies: 222
Views: 20348

Re: PIP-5048MK inverter

Now it's my turn to ask: @affer - what software are you using to get those graphs? i use this image https://diytechandrepairs.nu/raspberry-solar/ with some settings in grafana by my self. I wish this will work with my raspberry Pi3+ but it doesn't, i am still looking for a free one that does
by ojeysky
Thu, 05 Sep 2019, 00:33
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048MK inverter
Replies: 222
Views: 20348

Re: PIP-5048MK inverter

Mike See attached the Trend for today: Trend 2019 05 15.PNG It is interesting to see that there were more dips in the morning than in the afternoon. Also interseting to see while the Inverter was in Bypass mode no dips occurred. It might also be due to the batteries that were more charged in the af...
by ojeysky
Tue, 20 Aug 2019, 16:08
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hi, Hi, Could you tell me what app you are using for monitoring? Android or iPhone? dRdoS7 It's available on Android play store: https://play.google.com/store/apps/details?id=bleapp.volfw.watchpower Did you buy a Bluetooth adaptor for the Inverter? Thanks, dRdoS7 It's inbuilt, comes with the CC by ...
by ojeysky
Mon, 19 Aug 2019, 17:48
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

dRdoS7 wrote:
Mon, 19 Aug 2019, 13:02
Hi,

Could you tell me what app you are using for monitoring? Android or iPhone?

dRdoS7
It's available on Android play store: https://play.google.com/store/apps/deta ... watchpower
by ojeysky
Mon, 19 Aug 2019, 17:47
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

What is the setting number or abbreviation? It it's setting 13, this is usually called the "back to battery" voltage setting; I suppose it might be called the "back to discharge" setting, or similar. What do you recommend as an appropriate battery settings for a VRLA 24v battery set-up because I fe...
by ojeysky
Sat, 17 Aug 2019, 16:50
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Hello @coulomb

My GK series has a settings called battery discharge voltage, mine is at 27v and I have noticed that the inverter will switch to battery once it gets to 27v. Is this a normal behaviour?
by ojeysky
Wed, 14 Aug 2019, 09:41
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

I note that Ojeysky is in Spain, and August in Spain corresponds roughly to February in Launceston. I guess the system figured my origin based on the IP address geo-location, I have now updated my profile with country. Am located in Nigeria and it's the raining season here though we do have a sligh...
by ojeysky
Wed, 14 Aug 2019, 01:41
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Ah, I misunderstood, sorry. I thought you lost your loads at 5pm. I have no experience with the high voltage MPPTs. Perhaps other owners can post what voltage or time their MPPTs switch off. I agree that since the MPPT voltage range is given as 120-430 VDC, then the MPPT should still be producing p...
by ojeysky
Tue, 13 Aug 2019, 14:28
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Actually, I didn't realise at first (the second post is rather blurry), but the icon that is missing isn't the MPPT, it's the battery . So perhaps by 5pm your problem is overcharging of the battery. Do you have logs of battery voltage, or can you just watch the battery voltage towards the end of an...
by ojeysky
Tue, 13 Aug 2019, 14:14
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)
Replies: 206
Views: 20975

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

The intention of the equalisation settings is to periodically overcharge a flooded lead acid battery , so it keeps the cells equalised, and you just top up a bit more water as a result of the over-charge. You don't want to ever do this to a lithium battery of any chemistry. However, you have contro...