A little background, I am originally from the UK, I have used the PIP style inverters in the UK on a few off-grid installations, some single units and some single phase parallel installations. This was about 5 years ago and I never had any significant issues with these inverters, they were extremely cost effective and once commissioned proved to be quite reliable.
Fast forward to now, I currently reside in Phuket Thailand, we have had numerous issues with the grid supply so I decided to install an off-grid solar setup. We imported 25x 360w panels, 32x 280Ah LiFePo4 cells for 16S2P 48V 560Ah, 3x MKS-II-5KWB for 3 Phase operation, and we have a 3 Phase 30KVA generator. We also imported a Growatt 5KW grid-tie inverter to export if we are away from the property for extended periods.
The installation went reasonably well, I got the batteries installed and tested, I got the inverters mounted and configured, I started to commission the system and found numerous issues with the domestic wiring that took a while to resolve, electrical installations in Thailand are generally held together with spit and bubblegum. I had the system operating well, I have 8* panels to two inverters and 9* panels to the third, we were feeling very happy with the installation and then the problems started.
After approximately 3 days of reliable operation and no changes to the system one of the inverters exploded, the component on the SCC marked F1 (I presume a fuse) exploded, and also the majority of the battery side mosfets. At this point we presumed it was just a defective unit, so we had to re-wire the system, and the house for single phase and put the remaining two units into single phase - parallel operation. This was a bit of a pain in the bum, a lot of additional work, a loss of 1/3 of the solar harvest, but was sufficient while we negotiate with the supplier regarding replacement / ordering additional inverters (the alibaba suppliers are really not very helpful when it comes to customer service)
So after approximately 2-3 weeks of reliable single phase - parallel operation, again with no significant changes to the system, another inverter exploded. I was messaged by one of the Thai staff that the inverter was beeping, I looked and one inverter was displaying fault, I looked up the fault code and it referenced overload, the inverters are configured to auto recover from overload but this obviously did not work. I asked the Thai staff to observe me doing a system reset so they would be able to do this if I am not available. I proceeded to show him, Isolate the AC output, the AC Input, turn the inverters off, Isolate the solar, Isolate the battery, everything is off. Now to start everything up, turn on the battery, turn on the inverters, wait for inverters to start-up and Bang! the thing shot molten mosfet legs out the vents in furious anger! Scared the S@!? out of us!
So now I have removed this inverter and inspected inside, the failure is almost identical to the first unit, a small capacitor leg has burned out on the SCC board and almost all of the battery side mosfets have blown. I am now down to one inverter and I am feeling very reluctant to order replacements of the same, I am astounded at the way these units have failed, I know they are cheap but can things really be this unreliable! I also now do not have any grid supply as a fall back option, if this last inverter blows I will be stuck running the generator 24/7 for power and this is not acceptable. I can probably source another inverter locally as an emergency option if the worst comes to the worst.
Ideally I would like to repair / upgrade the two broken units I have, I will also be in communication with the supplier to see what they can offer but I do not have much faith in the Chinese to do this, the cost of returning the units and sending new ones makes this difficult. I have been reading some of the posts regarding the repair / upgrade of these units and various components, I am a little concerned that my units already have the CSD19505KCS mosfets and 80V capacitors. I will also need to try and test the mosfet drivers before just replacing them, and I still don't know why the units failed in such a catastrophic way in the first place. Is it possible to repair them without knowing what the original cause of the fault condition was?
This forum appears to have a wealth of information regarding the different variants of this inverter, I would welcome any advise on the next practical steps to take with these units before they end-up being salvaged for parts and build my own SCC from the components and have to buy alternative inverter. I am hoping I can make one good inverter from the two blown units, although I will have to replace the mosfets, any advice on testing the driver circuits would be helpful and any upgrade options other than the CSD19505KCS?
I will try and attach some pictures of my problems.

Original Installation

3Phase operation charging from solar and generator at 9KW



First SCC component failure

Original SCC F1 component for comparison

First FET failure

Another view of first FET failure

Single Phase fault warning

Single Phase fault warning

2nd Failure SCC cap failed

2nd failure FET

2nd failure FET another view
Thanks in advance for any advice you can offer.