Posted: Mon, 25 Jan 2016, 15:08
by Northland
Well I just had a basement full of smoke.

I was laying carpet upstairs and noticed smoke wafting up through a gap. I ran down and saw a haze, not thick. I could not see the source and flipped off all breakers. No cables, batteries or breakers were hot. The inverter wasn't hot. There was no fault led lit and output seemed normal. After a minute I turned breakers back on and restarted the inverter. Everything seems normal. It was on solar, pulling 1-1.5kw and load was 1.4kw.

Any ideas?

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 15:15
by Johny
My first guess is the electrolytic capacitors in the PIP. They could expire and vent and leave the inverter still functioning - for a while.

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 15:41
by offgridQLD
You should be able to smell it. Follow the smell if its strong smell from the PIP case then (TURN IT OFF NOW AND DISCONNECT THE BATTERY AND PV!!!!)Be for you potentially damage the unit more or burn your house down.

Kurt

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 15:57
by coulomb
Johny wrote: My first guess is the electrolytic capacitors in the PIP.

Could be. But electrolytic capacitors tend to make an unpleasant smell, quite distinct from the "burning resistor" smell you get from MOSFETs and, well, resistors Image

Was there a smell, and if so, what was it like?

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 18:04
by Northland
No smell that I noticed. I put a smoke detector above the inverter in case anything else happens

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 23:05
by rinaldoparaipan
Did you notice any leakeage below the inverter?
Do you see the PV icon on the display?

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 23:09
by Northland
No leakage. I did notice after restart, the pv icon disappear with a relay click then come back a few seconds later. But I have seen that on the remote about 20x before and thought it was normal

PIP-4048MS inverter

Posted: Mon, 25 Jan 2016, 23:52
by rinaldoparaipan
If the relay is clicking once, is a normal behavior due to the MPPT algorithm initializing.In my opinion is better to open the inverter case and check the 3300uF caps if they are swollen.Because if they will explode, will damage all the electronics around.I know how is it Image
I hope my English is understandable for you.

PIP-4048MS inverter

Posted: Wed, 27 Jan 2016, 01:49
by mmaritz
Hi Mike

I have PIP-MS_SCCMPPT1.24.rar installed as factory - is it worth upgrading to PIP-MS_SCCMPPT4.00.rar and so you know the benefits?

Thanks
Mark

PIP-4048MS inverter

Posted: Wed, 27 Jan 2016, 04:18
by coulomb
mmaritz wrote: I have PIP-MS_SCCMPPT1.24.rar installed as factory - is it worth upgrading to PIP-MS_SCCMPPT4.00.rar and so you know the benefits?
It's hard to say. I see differences to do with temperature monitoring, for example. The volume of code changes is small, but small changes can make a huge difference.

It's possibly better to ask some of the mega installers whether they've noticed any difference.

PIP-4048MS inverter

Posted: Wed, 27 Jan 2016, 06:08
by mmaritz
Thanks

PIP-4048MS inverter

Posted: Thu, 28 Jan 2016, 02:04
by Northland
OK so I've waited 48hrs for them to respond, which they haven't Image

I opened it up, did the fan swap. Could not see anything abnormal. Nothing smelly.

I noticed 6 relays inside. 3 on the main board, 2 on the mppt board, 1 on the comms board. All 12v coils. Anyone know what they do?

PIP-4048MS inverter

Posted: Thu, 28 Jan 2016, 11:53
by Northland
Thanks.

Well the Internet company called this morning saying our fibre box had been showing an error last few days. Mystery solved. Pity they didn't call yesterday

PIP-4048MS inverter

Posted: Thu, 28 Jan 2016, 13:11
by Northland
Obviously there is a 12v DC power supply, do you know where I could tap into it to run my voltage detectors? (100ma) really don't want to have to run a separate 12v plug pack

Also I would like to have an overide switch that would quickly switch to utility mode, without needing to go through the settings twice with delays (say my batteries are low and I want to run the kettle) would it be a case of disengaging the inverter relay (how....another relay in series?) and engaging the safety relay?

PIP-4048MS inverter

Posted: Thu, 28 Jan 2016, 15:54
by Northland
If relays disconnect the pvs, why have blocking diodes? 0.7v x 60A = 42w going to waste?


PIP-4048MS inverter

Posted: Thu, 28 Jan 2016, 23:06
by coulomb
Northland wrote: why have blocking diodes? 0.7v x 60A = 42w going to waste?

I think you mean bypass diodes, since no-one uses blocking diodes any more.
Also I believe that the diodes are Schottky types, which have a lower voltage drop of around 0.4 V near full load. But the reason for the bypass diodes is to do with protection of shaded panels from other panels in their string. See Weber's post on this topic.

[ Edit: Also, bypass diodes don't dissipate power except in circumstances where they're needed. ]

[ Edit2: clarified which type of diode (bypass) and corrected the panels they protect (others in the series string). ]

PIP-4048MS inverter

Posted: Fri, 29 Jan 2016, 00:33
by coulomb
coulomb wrote: Also, bypass diodes don't dissipate power except in circumstances where they're needed.

It seems you can get active bypass diodes now, so even though they are usually only needed during shading, you can reduce the losses in those conditions (for some situations, this will be a common occurrence):
http://www.digikey.com/en/articles/tech ... erformance

[ Edit: And now that I read more closely, I see they're claiming up to 0.5% improvement! Image I suspect there would be applications where the benefit is more substantial. ]

PIP-4048MS inverter

Posted: Fri, 29 Jan 2016, 13:00
by coulomb
Northland wrote: Obviously there is a 12v DC power supply, do you know where I could tap into it to run my voltage detectors? (100ma)
There is 12 V on the comm port; I don't know if it will provide 100 mA. See this pair of posts, but I haven't checked the 2015 model (not home at present). I'm hopeful that 12 V is still present on pins 7 or 4.
Also I would like to have an overide switch that would quickly switch to utility mode, without needing to go through the settings twice with delays (say my batteries are low and I want to run the kettle) would it be a case of disengaging the inverter relay (how....another relay in series?) and engaging the safety relay?

No need to operate the relays directly: there is firmware to do that safely.

You could run the PIP in Util mode all the time, and switch the incoming mains. It will still charge from PV whenever available, and use the inverter to supply power from the battery or PV when the mains is off. Alternatively, there is a serial command to change this setting; you could get an Arduino or Rpi or similar to squirt out that command when a switch is thrown, and the normal setting when that switch goes off. I think that Jaco's AICC software can do this from a computer.

[ Edit: +12 V on pin 7 of 2013 models, not pin 8, which is always ground/common. ]

PIP-4048MS inverter

Posted: Fri, 29 Jan 2016, 15:57
by weber
Excellent suggestions Coulomb.

Yes, isolated +12V is still present on pin 4 of the RJ45. (It was on pin 7 in early models, not pin 8 which has always been GND).

I just measured its voltage drop under load. At 35 mA it drooped from 12.91 V to 11.34 V, which suggests it has an internal resistance of about 45 ohms.

PIP-4048MS inverter

Posted: Sat, 30 Jan 2016, 20:17
by Northland
Here is the circuit diagram for my hot water regulator
Image

I wasnt sure what would happen if I put 230v on the output side of an SCR that didnt have 230 on input so I decided to use one instead of 5, remove the trim pot and configure resistors to vary the output of one SCR. It also kept mains voltage off the relays, and less live SCR terminals to worry about, so its safer.

It seems to work well. Relay 1 is basically a day / night. Each relay has a resistor on N.C or a short on N.O. The circuit carries through successive relays giving either a short (100%) or a sum of resistance (20-80%)
Going from full sun to overcast it drops from 5A (230) to 4 to 3 to 2 to 1, then when the sun comes back it goes back up.

I watched it all day and it automatically reduced HW load if the kettle went on or if the sun was behind a cloud. Battery current always seemed to be less than 3A in or out. On a rainy day instead of running a heavy load for 2hrs it will run a smaller load 8hrs. No strain on the batteries.

PIP-4048MS inverter

Posted: Sat, 30 Jan 2016, 23:26
by paulvk
coulomb wrote:
There is 12 V on the comm port; I don't know if it will provide 100 mA.


I am using this to run a small access point , router & rs232 to tcpip unit via a small switch mode regulator to get 5V dc
This output is not regulated it starts at about 15V so a switch mode regulator is need to stabilize the voltage
Its use is to run the remote control unit.
I am going to use it to run my web server interface to the inverter but my unit runs off 5V so it will not have a problem with its switch mode regulator.
This is the sort of regulator I/ am using
http://www.ebay.com.au/itm/LM2596S-Step ... Swl9BWJfYR

Northland
Replace your relays with opto couplers you will not need much current for them and you still get isolation.

PIP-4048MS inverter

Posted: Wed, 03 Feb 2016, 00:36
by edmundp
Hi All,

I have developed software to monitor the PIP-4048 inverter more effectively.

I would like to formally announce the launch of the SolarMon software.

The software changed in accordance with user requests the past few months - a personal thank you to one and all that contributed and tested.

The software has the following features:

Serial Connection to single Inverter
USB Connection to single Inverter
Data recorded every 5 seconds
Supports both the Victron BMV-700 and BMW-702 Battery Monitors
Resizes the app automatically for screen sizes 1024x600 and up
Dynamic Graphing & History Graphing
Data Export
In-app data viewing
Switch to Grid or Solar based on Battery Capacity and/or;
Switch to Grid or Solar based on 7 day Time Schedule
Daily Production & Usage Data
Automatic uploads to PVOutput.org with extended values such as Battery State of Charge, MidPoint Percentage, etc.
Custom Image display to personalize the application
All of the above is included in one standard version
Demo version available with very limited features to try out.
The software requires the .Net Framework 4.5.2 and MS SQL Express to run.

Please visit our webpage at www.solarmonitor.co.za for more information or contact us on info@solarmonitor.co.za.

[ Edit Coulomb: the link seems dead now. ]

We take user feedback very seriously.

Kind Regards,

SolarMon

PIP-4048MS inverter

Posted: Wed, 03 Feb 2016, 18:55
by Monkeytom
I have just received my second 4048 and was looking to parallel them has anybody on here done that, I was wondering if I could use the Gen start function to swith the second inverter on and not waist the second standby power till it was needed Thanks Tom

PIP-4048MS inverter

Posted: Wed, 03 Feb 2016, 19:34
by weber
I suggest doing a search within this topic on:

parallel pips

and then

parallel boxes

See "Topic Search" near the top of the page.

PIP-4048MS inverter

Posted: Wed, 03 Feb 2016, 20:45
by Northland
I came across this today, 95% cheaper than those other battery computers
J34 Free Shipping Capacity Tester Indicator Coulometer 35-80V 50A Lithium/Lead-Acid Battery Meter

http://s.aliexpress.com/7zmaEzQB