Post by Andreixda » Wed, 02 Nov 2016, 21:09

I mean Lucibus. Anyway a BIG THANKS to you and Coulomb. I put the Fw 72.60A and after 3 days my batt are happy now.( 2x12Vx150Ah VRLA) Image

Andreixda
Noobie
Posts: 5
Joined: Sat, 29 Oct 2016, 04:27
Real Name: Andrei ionescu
Location: Romania

PIP-4048MS inverter

Post by Andreixda » Wed, 02 Nov 2016, 21:16

I will try the solutions . Image

The biggest problem of these systems is monitoring the , as long as you see how they work , you can do maintenance on them and also save money, I am a telecom engineer and I am am used to monitor and analyze performance on power systems ( in telecom , this is the reason that chose 4048)

User avatar
lopez
Noobie
Posts: 9
Joined: Mon, 21 Jul 2008, 00:08
Real Name: John Lopez
Location: Blacktown

PIP-4048MS inverter

Post by lopez » Wed, 02 Nov 2016, 22:18

Fotosettore wrote: hi !
i already use sonoff to switch on-off relay to use surplus power from 4048, twilight switch and external fan switch.
First of all you need use LUCIBUS, that is a software i made to display
situation of 4048.
peppe
Thanks. Peppe, Just wanted to ask you whether Lucibus can upload data for monitoring to www.PVoutput.org.

User avatar
coulomb
Site Admin
Posts: 3780
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Wed, 02 Nov 2016, 22:34

Andreixda wrote: I put the Fw 72.60A and after 3 days my batt are happy now.( 2x12Vx150Ah VRLA) Image

I hope that's a typo, and you haven't put the patched firmware into a 24 V system (2 x 12 V). Presumably you mean 2 strings of 4 12 V modules.

I'm glad to hear that the batteries are happy. It's also good to see that at least some lead acid setups need the fix, it isn't just the radical hippy lithium worshippers Image that see the problem.

[ Edit: removed a paragraph that responded to a misreading. Added emoticon. ]
Last edited by coulomb on Wed, 02 Nov 2016, 17:15, edited 1 time in total.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

User avatar
Fotosettore
Noobie
Posts: 4
Joined: Sat, 18 Jun 2016, 12:59
Real Name: giuseppe de lorenzo
Location: italy
Contact:

PIP-4048MS inverter

Post by Fotosettore » Wed, 02 Nov 2016, 23:13

lopez wrote: Thanks. Peppe, Just wanted to ask you whether Lucibus can upload data for monitoring to www.PVoutput.org.

hi lopez !
no, i'm sorry Image
lucibus creates its own mdb database and it works exclusively with it.

in Italy it is rare that data is shared, because it could be used for different purposes and therefore almost all people do not share or upload them.
2 PIP4048MS inverters, 24 250W panels, 12 AGM 260A batteries.
Software LUCIBUS e synoptic monitor VIÁTOR.
Updated versions can be found on www.homoandroidus.com

User avatar
coulomb
Site Admin
Posts: 3780
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Wed, 02 Nov 2016, 23:18

Solar Junky wrote: Hey guys you got to help me have tried every thing to get the db9 cable to work??? ... any help would be AWESOME!

Here is something that caught me recently. There are a bunch of fake Prolific USB to serial converters out there, and the drivers have recently (in the last year or two) stopped supporting the older models (including hopefully for them all the illegal clones). I ended up buying another one some years back. and marked it as bad, but the writing wasn't terribly clear, and I forgot all about the issue. Recently when I went to grab my Prolific, I found the old one, and didn't realise it.

Maybe this isn't your exact problem, but it caught me, so it may catch others. The symptom is that when you plug in this bad device, Windows sees it, and you get the happy USB sound, and it loads a driver. But that driver crashes, and no software other than Device Manager can "see" the comm port. This is what Device Manager shows:

Image     Image

There is a tiny yellow triangle in the corner of the small icon; I've zoomed in to 150% of normal to show it moderately clearly. If you double click on the Prolific entry, you get the second screen. Here at least it's onbvious that Windows isn't happy with this device. (BTW, it can still be used successfully on Windows XP, but not Windows 7/8/10). Click on the Detail tab underlined in green above.

Image     Image

Now choose Hardware IDs from the drop down Properties list. You should get something like the second screen shot above. If you see REV_0300 as above, then it's the bad device, and you won't be able to use it with Windows later than XP. (Perhaps if you find a really old driver it might work for a time, but Windows will "update" the driver for you soon. You're welcome.) If it says REV_0400 or later, then you have a usable device.

Solar Junky, hopefully you saw my post about the flash tool only being able to see comm ports 1 through 9 (COMM1 to COMM9, not COM10 to COM99). It's right at the end of a page with lots of other threads being discussed, so it's possible you missed that.
Last edited by coulomb on Wed, 02 Nov 2016, 13:40, edited 1 time in total.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

paulvk
Groupie
Posts: 195
Joined: Fri, 23 Oct 2015, 23:45
Real Name: Paul
Location: Sydney

PIP-4048MS inverter

Post by paulvk » Thu, 03 Nov 2016, 00:23

"but Windows will "update" the driver for you soon"
You can stop windows doing this I use the old Prolific USB-232 on windows 8 & 8.1 with an old driver it has proven very stable
The best way to connect to the PIPs is the HLK-RM04 it gives you a virtual com port on your machine.

speriator
Noobie
Posts: 1
Joined: Fri, 30 Sep 2016, 20:56
Real Name: Marc
Location: Romania

PIP-4048MS inverter

Post by speriator » Thu, 03 Nov 2016, 09:44

Hello EveryBody

First of all, i'm french and sorry for my poor English :-(

I'd like to give many many many thanks for this incredible thread about this voltronic inverter ! It's full of very greats informations and it take me 2 full weeks to read every pages :-) :-) :-)

The subject : How to write a gateway between the inverter and watchpower with a raspberry (to target small price) to inject the inverter informations (battVoltage, PanelPower, etc... on my Europeen home automation bus system KNX, to manage the power loaders (for example to make cold water) when the sun is full or not. More generaly : how to use the excedeed sun power when the batt is full ?

So i started on august to develop with my dev boy, a Raspberry Native C++ application with this scopes :

- The raspberry must communicate with the inverter with Serial or USB port (it was the more difficult part of coding).
- The PC with watchpower must be connected on Raspberry with a cheap USB to SerialTTL to target the ACM0 IO port. Bluethooth will be disabled on PI3
- If WatchPower is not connected, the program must run on a standalone mode to send commands on the inverter.
- a xml config file for the KNX object configuation, because of many possible GroupAdress Configuration already instaled.
- a future TCP socket et HTTP communication, to target an IOS and Android app, on LAN mode and far away a cloud mode to manage your inverter when you are on the beach !

I've got a MPPSolar 3MPPT (MST version 75.1), and I discover some undocumented commands to get the values on Panel2 and Panel3, but the dev was firstly done on a simple MKS with 72.4 version

The TCP and HTTP are still to code, but we've solven all the rest of this PowerManagement Program

For the future, i target the put LUA scripting, and a TouchLCD 7" screen to see the information easier than now :-)

and many many other functionnality in this project for the future like BMS, but i prefer to stabilise what it done for now.

finally, I'd like to find some folks to help me to debug this first alpha version (I can give a IMG of an already installed System for PI3)

If you have interested, just give me a message

Many thanks.

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Thu, 03 Nov 2016, 12:24

Thanks webber & coulomb!!! & hi to everyone!
You guys are great help! Plan to soon do a video to thank some people that have helped me. if it's ok with you guys i'll mention you two in the youtube video??? Let me know if it's cool?
Last edited by Solar Junky on Thu, 03 Nov 2016, 01:25, edited 1 time in total.

User avatar
weber
Site Admin
Posts: 2626
Joined: Fri, 23 Jan 2009, 17:27
Real Name: Dave Keenan
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by weber » Thu, 03 Nov 2016, 15:53

Solar Junky wrote:if it's ok with you guys i'll mention you two in the youtube video??? Let me know if it's cool?
It's cool.

Following on from Coulomb's excellent post re USB to D9 cables. Here's a website with suitable drivers and instructions for installing them.
http://www.miklor.com/COM/UV_Drivers.php

One of the fathers of MeXy the electric MX-5, along with Coulomb and Newton (Jeff Owen).

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Fri, 04 Nov 2016, 20:15

Weber That information is good stuff!!

Yes most excellent post by Coulomb's!!!

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Fri, 04 Nov 2016, 20:24

pip 4048 grounding question???????
Have my inverter, batteries, negative side of the solar input grounded to the same ground grid uses. been like this for a long time so kinda forgot about it.... How Should it be grounded or will it be ok??? Have the positive side of solar input threw breaker & Negative fused with ground on inverter side of fuse.
Last edited by Solar Junky on Fri, 04 Nov 2016, 11:01, edited 1 time in total.

User avatar
coulomb
Site Admin
Posts: 3780
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Sat, 05 Nov 2016, 05:00

Solar Junky wrote: [ I ] Have my inverter, batteries, negative side of the solar input grounded to the same ground grid uses. been like this for a long time so kinda forgot about it.... How Should it be grounded or will it be ok???

The inverter itself will be grounded via the AC in cable, or if no mains connection, it should be grounded via the AC in or AC out earth.

I would not earth the battery or the PV, and certainly not both. I'm pretty sure that there are models [ edit: of the PIP/Axpert ] where connecting the PV negative to battery negative would cause the MPPT to be bypassed, so the panels would be continuously charging the battery and at poor efficiency. I suppose it's possible that it's doing that now, though I would think that there would be clues as well as alarms if that was the case.

So I would definitely not earth the battery or the PV array. Just leave both of them floating. You can earth the frames of the panels, but usually that's not a requirement when the panels are Extra Low Voltage (ELV, <= 120 VDC). Of course, that's completely different from earthing the PV input (negative or positive).
Last edited by coulomb on Fri, 04 Nov 2016, 18:02, edited 1 time in total.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Sat, 05 Nov 2016, 11:30

Just watched that video you posted thanks just the information needed!!
Last edited by Solar Junky on Sat, 05 Nov 2016, 00:35, edited 1 time in total.

paulvk
Groupie
Posts: 195
Joined: Fri, 23 Oct 2015, 23:45
Real Name: Paul
Location: Sydney

PIP-4048MS inverter

Post by paulvk » Mon, 07 Nov 2016, 01:17

I have noticed that my inverters seem to follow the mains frequency has anyone else noticed this?
Last edited by paulvk on Sun, 06 Nov 2016, 14:18, edited 1 time in total.

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Mon, 07 Nov 2016, 01:17

Thanks coulomb,
easy to disconnect it.
seems like it's working same as befor grounding solar & battery to earth
but did that some time ago and forgot about it.
Last edited by Solar Junky on Thu, 24 Nov 2016, 16:36, edited 1 time in total.

paulvk
Groupie
Posts: 195
Joined: Fri, 23 Oct 2015, 23:45
Real Name: Paul
Location: Sydney

PIP-4048MS inverter

Post by paulvk » Mon, 07 Nov 2016, 01:23

Note about earthing: As I have a 48V telco battery system as part of my battery racks the positive is earthed but no earthing on pos or neg from panels it has been working for nearly 2 years this way.

User avatar
coulomb
Site Admin
Posts: 3780
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Mon, 07 Nov 2016, 05:32

paulvk wrote: I have noticed that my inverters seem to follow the mains frequency ...
I believe it was Weber who stated not long ago that the inverters probably synchronise with the mains for the least difficulty when switching the loads to and from mains and inverter output. That seems quite plausible.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Tue, 08 Nov 2016, 07:19

Weber is my hero! fixed my d9 to usb problem.
My d9 cable went bad somehow???????? Did try a new one long time ago but took it back???? must have messed up the drivers then????
Now it's time to update firmware!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
YEAH!!!!!!!!!!! AWESOME!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
But need a mental break been working on this thing for days!!!!!!! lol!!!

Solar Junky
Groupie
Posts: 38
Joined: Sat, 15 Oct 2016, 04:00
Real Name: Danny
Location: Orlando

PIP-4048MS inverter

Post by Solar Junky » Tue, 08 Nov 2016, 07:23

Thanks weber have learned lots in the last few days.....

Tjadenw
Noobie
Posts: 16
Joined: Sat, 11 Jul 2015, 00:43
Real Name: Werner
Location: Cape Town
Contact:

PIP-4048MS inverter

Post by Tjadenw » Fri, 11 Nov 2016, 06:04

Is it possible to perform a voltage calibration on the 24 volt model that only have a USB port using access port ? I can fine lots of info on the PIP4048 voltage calibration using access port but nothing for the usb 24 volt 3kva model.

My 24 volt inventor seems to be .2 volts lower that the actual values when testing with a volt meter

User avatar
coulomb
Site Admin
Posts: 3780
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

PIP-4048MS inverter

Post by coulomb » Fri, 11 Nov 2016, 15:34

Tjadenw wrote: Is it possible to perform a voltage calibration on the 24 volt model that only have a USB port using access port ?
I believe that unlike the 48 V models, you can send commands to the 24 V models over USB. It's a virtual comms port, I think, even limited to 2400 bps.

But a quick check of the only 24 V firmware I have at present indicates that there is no BTA0-2 command, so if there is a calibration facility, it is very different to that of the 48 V models. Many of them also use a different processor (Freescale HCS08 versus a TI TMS320F2809). [ Edit: a later version I found does have the calibration commands, and does use a TMS320 processor. ]

I can fine lots of info on the PIP4048 voltage calibration using access port but nothing for the usb 24 volt 3kva model.
That seems to confirm my suspicion that they don't have calibration at all. [ Edit: I meant in the sense of a user instigated command based calibration. It may be possible to change an EEPROM value somehow, for a fixed scale change. ]

Your best bet for fixing this would seem to be finding the appropriate voltage divider resistor (or chain of resistors), and tweaking the values until it reads more accurately. Of course, you can't do much about drift and so on, but it sounds like a decent improvement could be had that way, if you are hardware inclined.

[ Edit: "They also use a different processor" -> "Many of them use a different processor" ]
[ Edit: "BAT0-2" -> "BTA0-2" ]
Last edited by coulomb on Fri, 11 Nov 2016, 04:36, edited 1 time in total.
Nissan Leaf 2012 with new battery May 2019.
5650 W solar, 2xPIP-4048MS inverters, 16 kWh battery.
1.4 kW solar with 1.2 kW Latronics inverter and FIT.
160 W solar, 2.5 kWh 24 V battery for lights.
Patching PIP-4048/5048 inverter-chargers.

User avatar
offgridQLD
Senior Member
Posts: 1825
Joined: Tue, 23 Jul 2013, 16:05
Real Name: Kurt
Location: Fleurieu Peninsula, SA

PIP-4048MS inverter

Post by offgridQLD » Mon, 14 Nov 2016, 14:27

A few of us in Brisbane took note of how ridiculously fast the shipping time was on a inverter that was aparently being shipped from Taiwan to Australia.

My first order several years ago was placed on a Friday and on the Monday I had a package at my doorstep. Though I didn't bother going through the tracking slips to look into it in detail.

It was mentioned that perhaps they have a storage facility in Au with local stock.

I now have a new project that requires another PIP4048. So I ordered a 2nd PIP last Friday afternoon online and tracked the delivery. I'm 99% sure they are actually being shipped from Taiwan and its just an incredibly efficient postal service. Living offgrid and relying on iverters to power your house and essentials being able to obtain a replacement or part over a weekend is not bad for a imported product.


Not to mention the shipping on this pip4048 was free and I was offered an extra 5% discount on the total price $949 AU delivered.

Image



Last edited by offgridQLD on Mon, 14 Nov 2016, 03:39, edited 1 time in total.

PGutti
Noobie
Posts: 3
Joined: Thu, 13 Oct 2016, 07:10
Real Name: Peter Güttinger
Location: Spain
Contact:

PIP-4048MS inverter

Post by PGutti » Mon, 14 Nov 2016, 23:59


Good to know! One question: Where did you order? MPP Solar or Voltronic?
(or is then name saying that Image

Tjadenw
Noobie
Posts: 16
Joined: Sat, 11 Jul 2015, 00:43
Real Name: Werner
Location: Cape Town
Contact:

PIP-4048MS inverter

Post by Tjadenw » Tue, 15 Nov 2016, 23:22

Thanks for the info Coulomb.

Do you know what the adjustment's on the SCC are for ?
Image