dRdoS7
Noobie
Posts: 11
Joined: Fri, 28 Sep 2018, 12:28

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by dRdoS7 » Sun, 21 Oct 2018, 13:08

Hi,
paulvk wrote:
Sat, 20 Oct 2018, 17:37
I have my ones two homes , four inverters mounted on ply wood I do not see a big risk of fire
They could be mounted with fiber cement board behind them which has a good fire rating
If mounted on a metal surface earthing and insulation need to be considered
Never even thought of fibro! Should have some in the garage. There'll be an air gap between inverter and fibro, so that should be OK.

Thanks,

dRdoS7.

PS. 2 homes & 4 inverters? Capitalist or Mormon, or both? :lol:

paulvk
Groupie
Posts: 159
Joined: Fri, 23 Oct 2015, 23:45
Real Name: Paul
Location: Sydney

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by paulvk » Mon, 22 Oct 2018, 20:30

Actually 6 inverters 2 spares got them early at a good price.
Big battery bank second hand
2nd home battery bank was new but it replaced a previous 48v ups before I thought about getting solar so not ideal.
If I just wanted to reduce power bills I could have just got grid solar installed but there is no fun in that :D
Fibro yep that will not burn and that stuff sold in Australia as hardi plank would resist an acetylene torch!

dRdoS7
Noobie
Posts: 11
Joined: Fri, 28 Sep 2018, 12:28

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by dRdoS7 » Tue, 23 Oct 2018, 04:46

paulvk wrote:
Mon, 22 Oct 2018, 20:30
If I just wanted to reduce power bills I could have just got grid solar installed but there is no fun in that :D
Unless you have PFiT until 2024!

And a SPS!

I started with a UPS as well.

dRdoS7.

paulvk
Groupie
Posts: 159
Joined: Fri, 23 Oct 2015, 23:45
Real Name: Paul
Location: Sydney

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by paulvk » Tue, 23 Oct 2018, 18:15

I think you may have misunderstood it was not a 240V ups I had, for over 15 years a 48v DC system
and I still have it running 48v to 12v for various gear and some that runs straight off 48v.

dRdoS7
Noobie
Posts: 11
Joined: Fri, 28 Sep 2018, 12:28

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by dRdoS7 » Wed, 24 Oct 2018, 04:35

Hi,
paulvk wrote:
Tue, 23 Oct 2018, 18:15
I think you may have misunderstood it was not a 240V ups I had, for over 15 years a 48v DC system
and I still have it running 48v to 12v for various gear and some that runs straight off 48v.
Uninterruptible Power Supply?

I don't see how there's a misunderstanding. Surely, if it is there to supply power when the main supply of electricity fails, it's a UPS, otherwise it's just a power supply.

My UPS was 48v, output 240V AC. Got tired of power failures, so put it in for "vital" appliances, it gave many hours of backup. :D

dRdoS7.
Last edited by dRdoS7 on Tue, 30 Oct 2018, 10:45, edited 1 time in total.

aim120
Noobie
Posts: 1
Joined: Sun, 18 Nov 2018, 17:23

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by aim120 » Wed, 21 Nov 2018, 23:09

Is there a patched firmware version for the Axpert VMII 5kva (PF1.0, PV 120v-450V) aka PIP5048GE

User avatar
weber
Site Admin
Posts: 2505
Joined: Fri, 23 Jan 2009, 17:27
Real Name: Dave Keenan
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by weber » Thu, 22 Nov 2018, 04:43

aim120 wrote:
Wed, 21 Nov 2018, 23:09
Is there a patched firmware version for the Axpert VMII 5kva (PF1.0, PV 120v-450V) aka PIP5048GE
No. Sorry. We need a manufacturer's firmware update file for it before we can do that, and no one has sent us one. All available patched firmware is listed in the Firmware section of the index page.
One of the fathers of MeXy the electric MX-5, along with Coulomb and Newton (Jeff Owen).

serpentus
Noobie
Posts: 2
Joined: Wed, 12 Dec 2018, 04:59
Real Name: Alejandro

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by serpentus » Wed, 12 Dec 2018, 05:12

[ Note from Coulomb: I accidentally edited this post when I meant to reply to it. This is a hazard of being a moderator. I've attempted to undo that, but I have missed some parts of the original post. @serpentus, I'm sorry if I have damaged your first post. I've reposted my accidental-edit as a proper reply here (next page). Unfortunately it now appears after your response to it. ]


I saw the Axpert MKS II 5K (the one with 450VDC MPPT) ( http://www.voltronicpower.com/oCart2/in ... uct_id=132 ). I wanted to ask if you guys know if this inverter has the premature floating bug issue. The inverter is the latest model ( that is what the dealer told me), just arrived in Chile. ...

Also I read in another forum that the Axpert invertors should not be used over the 40% of the rated output. Is this true? And why?

I want to know this before buying it. Or else I'll look for another brand.

EDIT: Same questions for the Axpert MKS 4K-48.

serpentus
Noobie
Posts: 2
Joined: Wed, 12 Dec 2018, 04:59
Real Name: Alejandro

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by serpentus » Wed, 12 Dec 2018, 12:33

Well... Now I'm in trouble, can't find a decent inverter. Xantrex, but it is expensive, out of my budget. Victron, do not like the one they are selling here, and it is to expensive (~USD 2.118).....

Will keep looking for another one. But it seems I'll have to import one myself.

Thank you very much for your answers and time.

User avatar
coulomb
Site Admin
Posts: 3459
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by coulomb » Thu, 13 Dec 2018, 09:53

[ Note: Serpentus' post above, is a response to the following, which originally appeared when I accidentally edited his earlier post. My apologies for these two posts now being in reverse chronological order. ]
serpentus wrote:I saw the Axpert MKS II 5K (the one with 450VDC MPPT) ( http://www.voltronicpower.com/oCart2/in ... uct_id=132 ). I wanted to ask if you guys know if this inverter has the premature floating bug issue. The inverter is the latest model ( that is what the dealer told me), just arrived...
Sadly, almost certainly it does have the premature float bugs. Worse, there isn't a patched version of this firmware to correct it.

Voltronic Power: it's so simple! You've swapped float and absorb/CV voltages in your source code somewhere, and have been perpetuating that error in every inverter-charger firmware since. And it's so simple to demonstrate the problem, so you can't pretend it doesn't exist!

Also I read in another forum that the Axpert invertors should not be used over the 40% of the rated output. Is this true? And why?
That's nonsense. However, these are low-end inverters, and they do cut corners on the specifications for some of the components. That's why Weber and I always replace the MOSFETs and capacitors in all our inverters. That gives them more voltage "headroom" and the capacitors (which protect the MOSFETs) a lot more life. Of course, most people don't have the technical capacity to do this, so they just take the chance, and simply replace the inverter when it fails. As long as it's not a mission critical application, this probably makes economic sense.
I want to know this before buying it. Or else I'll look for another brand.
Brands like Victron and SMA have far better components inside. But the last time I looked at this (admittedly that's many years ago now), the next best inverter was many times the price of these Voltronic Power units. So for us, patching the firmware and upgrading some components was worth the extra effort. Maybe that's no longer the case.
EDIT: Same questions for the Axpert MKS 4K-48.
The same comments apply to all their inverter-chargers, although their Infini series (hybrids) may be different. I don't have enough experience to comment there.

[ Edit: this was originally posted a few posts ago, when I erroneously edited instead of quoted the original post. }
Learning how to patch and repair PIP-4048 inverter-chargers and Elcon chargers.

jacobbloy
Noobie
Posts: 1
Joined: Tue, 18 Dec 2018, 20:40
Real Name: jacob bloy

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by jacobbloy » Tue, 18 Dec 2018, 20:47

is there any one who is working on firmware for the newer models of the pip inverters. I purchased the pip-5048GK. there is a specific battery that I would like to use and the voltages are to low to be used with my inverter.

30v-42v discharge and 42v charge.
the pip lowest voltage for discharge is 44v and 42v under voltage cutoff.

MrTechSantiago
Noobie
Posts: 1
Joined: Tue, 18 Dec 2018, 22:29
Real Name: Jose O Santiago

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by MrTechSantiago » Tue, 18 Dec 2018, 22:42

Team,
I own a PIP5048GK in Puerto Rico creating a split phase 240/120V using a toroidal 5KVA autotransformer. I Previously had PIP4048GE PF1.0 version and PIP5048MG PF1.0

Sorry if Iam posting in the wrong forum but I want to know if someone are working in a custom firmware for PIP5048GK. Also Iam software developer and Iam working in a custom software(see attachment image) to communicate with inverter via modbus. I have almost done all software interface, I have usb to modbus communication cable but I dont know too much how to start a communication with inverter and its communication protocol.

If someone are in a project like this and can help me, I will appreciate that. Thanks a lot
unnamed.png
Custom Software interface
unnamed.png (66.75 KiB) Viewed 554 times

User avatar
coulomb
Site Admin
Posts: 3459
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by coulomb » Wed, 19 Dec 2018, 07:03

jacobbloy wrote:
Tue, 18 Dec 2018, 20:47
is there any one who is working on firmware for the newer models of the pip inverters.
No. It seems that Weber and I are the only two working on firmware patches for any Voltronic Power inverters, and we don't have access to any firmwares for these models. We also don't have any interest in them, and would prefer not to encourage others to use them.
I purchased the pip-5048GK. there is a specific battery that I would like to use and the voltages are to low to be used with my inverter.
30v-42v discharge and 42v charge.
the pip lowest voltage for discharge is 44v and 42v under voltage cutoff.
Sorry, but that battery isn't suitable for that inverter, or likely any nominal 48 V inverter. To get 5000 W from 30 VDC, ignoring sagging and losses, you'd need 167 A, and the front end simply isn't designed to carry that sort of current. So even if you could butcher the firmware to accept such a low battery voltage, it would very likely blow up the inverter.

[ Edit: Reworded from "would only fix charge bugs" to "prefer not to encourage others". ]
Learning how to patch and repair PIP-4048 inverter-chargers and Elcon chargers.

User avatar
coulomb
Site Admin
Posts: 3459
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by coulomb » Wed, 19 Dec 2018, 07:09

MrTechSantiago wrote:
Tue, 18 Dec 2018, 22:42
Sorry if Iam posting in the wrong forum ...
I've moved the post to a new topic.
but I want to know if someone are working in a custom firmware for PIP5048GK.
If there are, hopefully they'll find this topic and let you know. But I don't think it's likely. The art of working with executable / binary files, even with assembler code, seems to be dying.
Learning how to patch and repair PIP-4048 inverter-chargers and Elcon chargers.

dRdoS7
Noobie
Posts: 11
Joined: Fri, 28 Sep 2018, 12:28

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by dRdoS7 » Thu, 20 Dec 2018, 13:27

Hi,

I noticed yesterday, and again today, that my 5048MG was pushing the battery > 64V. It's not problem for me, as I have NiFe batteries, and the higher the better! Absorb is set to 64V. EQ is disabled.

Today it did it for about 1/2 hr, yesterday only a few minutes.

I have a 2nd SCC (a Classic 200), but the output of that was at 0 when I checked. The Classic's Absorb setting is 64.2V.

It's the first time (OK, second) I have seen this since I've had it connected (05Nov2018).

I can't add attchments, so uploaded to an image site instead.

Yesterday:

Image

It actually was higher (65V) yesterday, but I wasn't fast enough to get a screenshot.

Today:

Image

Should add that the Classic was in Absorb both times, before and after the excursion.

Thanks,

dRdoS7

User avatar
coulomb
Site Admin
Posts: 3459
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by coulomb » Thu, 20 Dec 2018, 19:42

dRdoS7 wrote:
Thu, 20 Dec 2018, 13:27
I noticed yesterday, and again today, that my 5048MG was pushing the battery > 64V.
PIPs are not great at battery voltage regulation; under- and overshoots are common. I suspect that they don't do much about the classic control problem of integral windup.
Today it did it for about 1/2 hr, yesterday only a few minutes.
I think you need to get that voltage down; I have no idea what the voltage margin is on the 64 V models. As the capacitors protecting the MOSFETs age, that margin will presumably come down.
I have a 2nd SCC (a Classic 200), but the output of that was at 0 when I checked. The Classic's Absorb setting is 64.2V.
I have a similar setup, but with my PIP-4048. It's not an ideal setup, but I'm a cheap old man. I found through experience that I really had to have the second SCC get right out of the way while the PIP finished the absorb cycle on its own. So I set the second SCC's absorb voltage to be a few tenths of a volt lower than the PIP's absorb voltage setting. Similarly, I set the second SCC's float voltage setting a little lower than the PIP's float voltage setting. So they worth together for most of the bulk stage, the PIP does the end of the bulk stage and all of absorb (I have LiFePO₄ so that's only about 15 minutes), and most of the time in float, the PIP does all the work. When there is a larger load during float, the battery voltage drifts lower, and the second SCC starts to take some of the load. I don't have equalise turned on. It works well enough for me. I don't know if you'll be able to find a compromise like that for your battery situation.
It's the first time (OK, second) I have seen this since I've had it connected (05Nov2018).
You need to find out if it was really happening and you didn't notice it. Do you have logging?
Learning how to patch and repair PIP-4048 inverter-chargers and Elcon chargers.

Carricondo
Noobie
Posts: 1
Joined: Sun, 23 Dec 2018, 19:58
Real Name: Francisco

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by Carricondo » Sun, 23 Dec 2018, 20:04

Before reading this forum line, I installed Firmware 73b on my PIP 5048 MG 450v inverter.
Now when it turns on, error 02 appears for a high temperature for a few seconds and switches off.
Is it possible to reinstall the previous firmware without going through technical support? :oops:

User avatar
coulomb
Site Admin
Posts: 3459
Joined: Thu, 22 Jan 2009, 20:32
Real Name: Mike Van Emmerik
Location: Brisbane
Contact:

Re: PIP-5048GE, PIP-5048GK and PIP-5048MG inverters (with unsafe SCC)

Post by coulomb » Sun, 23 Dec 2018, 20:27

Carricondo wrote:
Sun, 23 Dec 2018, 20:04
Now when it turns on, error 02 appears for a high temperature for a few seconds and switches off.
I'm sorry to hear that. It's most unfortunate that while there is some protection against incorrect firmware updates, this is not one of them.
Is it possible to reinstall the previous firmware without going through technical support? :oops:
Alas, no. As far as I'm aware, there is no firmware updates for these machines at all. You'll have to go through your supplier.
Learning how to patch and repair PIP-4048 inverter-chargers and Elcon chargers.