Page 81 of 102
Changing the output voltage
Posted: Sat, 10 Feb 2018, 11:27
As far as I know, the output voltage setting procedure is not documented at all. My initial research indicated that you have to send it a "V220" command to change the output voltage to 220 V. However, this turns out to be dead code in the firmware; it has no effect other than very slightly wearing out the EEPROM.
Subsequent research reveals that you need a POPV2200 command to change the output voltage to 220.0 V. The other two possibilities are POPV2300 and POPV2400 for 230 V and 240 V respectively.
The on/off switch at the bottom of the inverter needs to be in the off position for this command to succeed, otherwise the inverter will NAK the command and ignore it. I believe that with the switch in the off position, the inverter will shut down in about a minute or so, so don't switch off till you have everything ready.
You will need a computer with a USB port and a USB to RS232 adapter, and a communications program capable of sending 8-bit characters. The 8-bit characters are required for the CRC characters that are needed at the end of each command.
[ Edit : the USB to RS232 adapter needs to connect to the inverter-charger via the provided D9 to RJ45 cable. ]
Choose one of these methods (or use some other communications program that is capable of sending 8-bit characters):
  • See the end of this post for setting up Tera Term. Note: to enable 8-bit character transmission, you need to find and edit the initialisation file, as per the instructions in the linked post.
    Having set up Tera Term, enter the following for 220 V output:
    shift+P shift+O shift+P shift+V  2 2 0 0  m right alt+shift+@ enter
    For 230 V:
    shift+P shift+O shift+P shift+V  2 3 0 0  shift+Z right alt+p enter   (CRC corrected)
    For 240 V:
    shift+P shift+O shift+P shift+V  2 4 0 0  right alt+shift+_ (underscore, usually shift "-") ` (back quote, usually to the left of the "1" key) enter
  • Alternatively, this post has the CrcGen app for calculating the CRCs and pasting the command with CRCs as hexadecimal into the clipboard. Use with Realterm. NOTE: I could not figure out how to turn on Realterm's hex mode, so if using Realterm, instead of using Scott's CrcGen app, you could paste one of the following strings into the appropriate drop-down box on Realterm's Send tab:
    0x50 0x4F 0x50 0x56 0x32 0x32 0x30 0x30 0x6D 0xC0 (for 220 V; don't copy these comments in brackets)
    0x50 0x4F 0x50 0x56 0x32 0x32 0x30 0x30 0x5A 0xF0 (for 230 V; CRC corrected)
    0x50 0x4F 0x50 0x56 0x32 0x32 0x30 0x30 0xDF 0x60 (for 240 V)
Either way, you should see an "(ACK9 " response (no quotes), and not a "(NAKss".
Unfortunately, I am not in a position to test the above, so I may have slipped up. The commands themselves have been tested, running at 240 V overnight, and at 220 V for several days (thanks, Weber!), but we have a different way of sending the commands, with CRCs generated automatically by our BMS master.
When paralleling machines, they all have to be set to the same voltage. If they are not, an undocumented Error 73 results. The obvious solution is to manually change the voltage settings as required.
If you were running WatchPower, you'll have to exit it (not just close the window). If unsure, see the how to update firmware post for exactly how.
[ Edit: @ is usually shifted. ]
[ Edit: corrected ACK and NAK responses. ]
[ Edit: CRCs calculated in BMS master, not Node-red. ]
[ Edit: arrgh! CRC was wrong for the POPV2300 command. Thanks, Weber! ]
[ Edit: added note re Error 73. ]
Re: PIP-4048MS inverter
Posted: Sat, 10 Feb 2018, 15:50
by lion6912
Thanks coulonb. Very very good.
I can try to change 230V to 220V, but I dont know Tera Term, CrcGen, realterm.
It is possible to read EEPROM ?
I have launch Tera term, I select COM1, and I have a dark screen.
What do you do now ?
Posted: Sat, 10 Feb 2018, 16:27
by lion6912
I try realterm, but Where can put " 0x50 0x4F 0x50 0x56 0x32 0x32 0x30 0x30 0x6D 0xC0 "
Posted: Sat, 10 Feb 2018, 16:57
I try realterm, but Where can put " 0x50 ... "
First, ensure that you have the correct bit rate and port selected, using the Port tab (brown):
Realterm set 220Vb.png (15.02 KiB) Viewed 5105 times
Note that 2400 is right down the bottom of the "Baud" drop-down box. Select the appropriate port; it varies from machine to machine, and also depends on which USB port you plug your USB to RS232 adapter. (I forgot to mention that you need to connect to the inverter via the supplied D9 to RJ45 cable; I've now edited the original post to include this step.) I usually use Tera Term to tell me which port my USB to serial adapter is on; for me it's port 10 but it could be anything else for you. Sometimes Realterm includes a description of the device connected to the port, sometimes it doesn't. You may have to press Open or Change to actually connect; you'll know when it does connect by the message in the bottom right corner of the Realterm window:
Realterm set 220Vc.png (7.29 KiB) Viewed 5105 times
If it says "Port: closed" then you haven't opened it successfully yet. The "10" could be any number, of course, depending on your computer.
Now go to the Send tab (red highlight):
Realterm set 220Va.png (22.03 KiB) Viewed 5105 times
Tick the two boxes indicated in green. Paste into the dropdown box where the blue is, using the standard Windows key combination of ctrl + v. Then press the Send Numbers button (orange). You should see "(ACK9" as a response. If you see "(NAKss", make sure that the inverter's on/off switch is off. If you see no response, check the bit rate and port settings, the USB to RS232 adapter, and cable to the inverter.
[ Edit: added third screenshot. ]
Posted: Sat, 10 Feb 2018, 17:26
by lion6912
It is GREAT.
Very thanks Mister coulomb.
I am at 220V.
But if I can manualy 220V, I could put over than 58.4V for battery ?
Posted: Sat, 10 Feb 2018, 18:37
I am at 220V.
Well done!
There is a special-order model of the PIP-4048 that allows up to 64 V of charging, if you think you really need to go beyond 58.4 V. I don't know anything else about it, not even a name for it. I assume it has different MOSFETs and higher voltage capacitors, and different firmware.
The attachment is from http://www.voltronicpower.com/oCart2/in ... uct_id=132 .
Posted: Sat, 10 Feb 2018, 21:17
by lion6912
I dont want reach 64V but only near 59.4V . But I dont want crah mosfet or capacitors.
Thanks
PIP-4048MS inverter
Posted: Mon, 12 Feb 2018, 14:56
Release Version of Patched Firmware 73.00b
[Edit: This post was originally for the beta version of 73.00a, but after being in use for 6 weeks, and being downloaded 38 times for LFP and 55 times for other chemistries, we updated the zip files to "release" status. Then a few days later we learned about a problem where 73.00 (both original and patched) would stop working after 60 days (with fault code 90) when run on older hardware. 73.00b fixes that problem. It was a one-word change, so we didn't bother with a beta.]
Weber and I have finally finished testing our patched firmware based on factory firmware version 73.00. Hardware that comes with factory firmware 73.00 has a neutral to earth relay, which is active only when the inverter is in battery mode. 73.00 also modifies the behaviour of the fans, spinning the fans even at no load, and more vigorously during heavy solar charging. There may be other improvements as well. 73.00 is parallel compatible with some older firmwares: 52.30, 72.40, and 72.6X, but not 72.70.
This patched firmware has all the same patches as 72.70c and earlier patched firmwares, including Dynamic Current Control and AussieView™. Naturally, this includes fixing the infamous premature float bugs.
As before, there is an LFP (Lithium Ferrous Phosphate) version, and the "all other chemistries" version (LC for Lead aCid, Lithium Cobalt blends, and lithium titanate).
Note: This firmware is only suitable for the 48 V models with a single low-voltage MPPT and a power factor of 0.8 (4 kW / 5 kVA), not those with dual or triple MPPTs or a power factor of 1.0 (5 kW / 5 kVA), and not those with a maximum PV array open circuit voltage greater than 145 V DC.
dsp_LF1_73.00b.zip
(1.53 MiB) Downloaded 152 times
For lead acid (24S), lithium cobalt-blends (LCO, NMC, NCM, NCA) (14S), and lithium titanate (LTO) (21S)
dsp_LC1_73.00b.zip
(1.53 MiB) Downloaded 242 times
Note: Lithium ferrous phosphate (LFP) is the same as lithium iron phosphate or LiFePO₄. The name "lithium ferrous phosphate" is preferred, as it avoids the confusion between "iron" and "ion".
For details on reflashing, and what hardware this firmware will and won't run on, see the 72.70b reflashing instructions, but ignore the files there.
[ Edit: Links to text files for DCC and AussieView™ ]
PIP-4048MS inverter
Posted: Mon, 12 Feb 2018, 18:01
Posted: Wed, 14 Feb 2018, 10:25
by al76
weber wrote:
Wed, 31 Jan 2018, 15:19
al76 wrote:
Wed, 31 Jan 2018, 13:57
The OC voltage reported by the Pip is about 130v Once mppt kicks in with charging it drops to about 110v
From this graph you can see that Volts sits about 130v until about 10am the mppt/charging kicked in.
I turned off the solar about 4pm ( on graph you can see Volts drop to zero) to try and change the string but I had a connector issue then it it started raining :(
Hi Alan, If your connector issue was difficulty in getting MC4 connectors apart, I note that a 16 mm (or 5/8") open-end spanner works well to compress the barbs and allow them to come apart. Much better than fingers (too fat to fit in the notches), and much better than pointy nose pliers (jaws not parallel). But even with the spanner compressing the barbs, it can take a lot of pulling and wiggling to get them apart.
I turned the solr back on and as you can see the V went back to about 125v and the relay just clicks away again.
Given the OC volts is well below max of 145v is it possible there is some issue with the pip?
I'll be adding some more panels soon so I may have to wait to do the string mod test.
It does seem that your PIP is more sensitive to high voltage than is claimed in the manual, but for all I know, they may all be like that. What are your U1 and U2 firmware version numbers?
But no matter whether the PIP is out of spec or not, there is no doubt that the optimum number of 72-cell panels in series, for a PIP-4048MS, is 2. Please just do the experiment.
I finally changed the strings this morning to 2 strings of 2 panels was 2 strings of 3. The problem persisted with the relay clicking away. After approx an hr the charging started.
Posted: Wed, 14 Feb 2018, 12:13
by paulvk
Have a problem with 72.70 the Max. Charging Current setting has become a max current setting for solar charger so if you set it at 30amps that is all the solar charger will put out instead of being max charge to battery.
Only found this out because I loaded them up to 4500watts and was getting a battery discharge then saw that only 30amps of total PV was there.
Two pips in parra with 225ah of LA flooded.
Posted: Wed, 14 Feb 2018, 13:47
OK. So now we know there is definitely something wrong with your machine. This is definitely not expected behaviour. My next suspect is the relays in the SCC. Maybe their contacts are badly burned and making intermittent contact?
Posted: Wed, 14 Feb 2018, 13:56
It sounds like you have the Solar Balance parameter [31] set to Sbd. If so, you need to set it to SbE (the default).
See the bAL [31] section of the AussieView manual or page 23 of the manufacturer's manual.
Posted: Wed, 14 Feb 2018, 19:17
by al76
Is it worth following this up with mpp solar or move fwd with buying another unit and have this unit repaired in Aus? I was planning on a parallel system plus I will be needing a second independent system soon anyway.
Posted: Wed, 14 Feb 2018, 19:39
I can't really advise you on such decisions. Except to say that I don't see that you have anything to lose by raising the problem with MPP Solar.
How long has the PIP-4048MS been in use? Could there be a fault in the isolation device between your PV array and the PIP?
Posted: Thu, 15 Feb 2018, 22:19
by simat
I am really impressed by the amount of excellent information in this thread and especially at all the work done by Coulomb and Weber. This is forums at their best! Thank you!
I have been asked by a friend of a friend who I designed and installed an LFP based off grid system for in 2013 if I would help him get an off grid system up and running.
This thread has made me think that it might be worth considering using the PIP4048MS or maybe the 5048 rather than a separate charge controller and inverter from more mainstream manufacturers. I am considering the Victron Phoenix inverters and EPSolar charge controllers.
The price of the PIP4048MS makes it worthwhile buying a spare and all the information in this thread will make it easier to interface my BMS to the SCC and inverter in the PIP and fix it if there are any problems.
My plan would be buy two units, run one for 3-5 years or until it blows up (hopefully not!) and then swap it with the spare. I would replace the main caps as detailed in this thread in the unit that I had swapped out.
I was thinking of configuring the LFP battery as 15s rather than the normal 16s to drop the voltage a bit. Only issue I can see with this is that it will increase the current. Which is preferable, decreasing the voltage stress or increasing the ripple currents and component temperatures due to the increased current?
I wanted to shut down the SCC via a signal from my BMS. Am I right in thinking that I can do this by sending a command to the PIP to raise the bulk and float voltages, or is there another way to do this?
I also wanted to be able to shut down the inverter. After reading the thread a few times! I am not sure if this can be done by sending a command but is possible by simulating the On/Off switch on the PIP being turned off, am I right?
Simon
Posted: Fri, 16 Feb 2018, 12:33
by T1 Terry
Hi Simon, I've had success with the 15 cell arrangement charging via a PWM controller using nom. 12v panels (18v Vmp) in series. The 24v units come in 5000va (4kW) models and they don't seem to have current rated issues so I can't see the 48v model having issues. The days of needing high voltage battery packs to reduce the current requirements really date back to the lead acid battery days, using LYP cells where high current draw is not an issue the days of requiring the use of a 48v battery pack and charging components might really be a carry over rather than a necessity.
I recently installed a 32 x 200Ah cell battery (4p8s 24v) with a 4kW PiP inverter and 5.6kW of solar and the system is out performing any and all expectations with none of the herding feral cats using Dingoes type problems the 48v systems seem to enjoy.
Posted: Thu, 01 Mar 2018, 13:24
by lopezjm2001
Beta Version of Patched Firmware 73.00a
Thanks for the great work you guys do, Coulomb and Weber. I updated my PIP4048MS to your latest beta firmware a couple of days ago. Not sure whether I needed it or not as I was running the latter version.
You can see a graph of your beta 73.00a firmware at work at https://drive.google.com/open?id=1U7GgT ... pzOlgMBowp, it works well. Can also view my PIP4048MS at https://emoncms.org/dashboard/view?id=33822 as is setup for public viewing. You can see how it goes into float mode at the right time. Does bulk charge followed by float mode even on cloudy days. No problem.
I like how my PIP4048MS LCD screen now shows the temperature of the unit... nice. 8-)
You guys should try to get crowd funding for this..
Posted: Sun, 04 Mar 2018, 09:46
Thanks for that, lopezjm2001. As we don't ask for money, it is kind words like yours that keep us going. I'm glad you like the "AussieView" LCD improvements. I'm surprised at how little feedback we've had about those. But we try to assume: "No news is good news". :)
Posted: Mon, 05 Mar 2018, 20:12
by paulvk
I have 72.70 running on the systems and the battery performance appears to be much better but note I also have the 9 panels with the e-smart3 as well.
The battery is staying at a higher voltage for much longer while under discharge at night, the balance of the current from/to the banks is much better.
As a companion to the PIP the E-smart3 is a good match giving the extra 40amps to take solar to 100amps which gives the system enough to run the loads and charge the battery properly.
As far as the now usable LCD goes I have not had enough time to do a lot with it but it is nice to be seeing batt volts , solar current and batt current on two PIPs
Note I have VRLA
I am going to try and find time to finish the remote display I started on which uses a dotmatrix LCD to display most of the parameters all at once from the QPIGS command.
Posted: Wed, 07 Mar 2018, 05:29
by Tejota
There is a special-order model of the PIP-4048 that allows up to 64 V of charging, I assume it has different MOSFETs and higher voltage capacitors, and different firmware.
MOSFETS in PF1 5kW up to 64V charging are TK100E08N1
I have seen them through the grid of holes. I dont know if there are 16 or more. I cant watch capacitors.... I would have to open the device invalidating the warranty.
A question about parallelized pips: If mosfets/igbts in one unit of the cluster fail, what happens in the other units of the cluster?
Regards.
Posted: Wed, 07 Mar 2018, 06:23
Wow! So these are 80V MOSFETs with Vgs=0, but only 60V with Vgs=-20 V. The datasheet doesn't say what voltage is safe with intermediate gate voltages, but suggests (to me) that with any significant negative gate voltage, which I assume is standard, that the limit is 60 V. So there must be a non-standard gate drive for these. Or I'm misunderstanding the datasheet.
Well sleuthed! Maybe an optic fibre camera next? 😎
Is there a special firmware revision number? I imagine they would want to distinguish the high voltage versions from others, yet indicate what other features and/or bug fixes it has in common with the nearest non high voltage version.
A great question. Firstly, I'll consider MOSFET failure. I assume that the battery is effectively shorted while the MOSFET leads (the real battery fuse) are melting, which would protect other inverter units in the cluster. But when the last MOSFET lead lets go, the voltage across the battery terminals to the other units would suddenly increase, and I imagine that there would be an inductive overshoot that would severely test the capacitors and MOSFETs in the other units of the cluster. This spike in voltage might or might not be enough to take out some or all of the other units.
Secondly, if the IGBTs fail, then the 400V bus is shorted, which might or might not take out the MOSFETs of the same unit, depending largely on the health of the battery side capacitors (and probably also the health of the bus capacitors as well). This would happen via a surge through the high frequency transformer coupling the bus and battery circuits. This would then propagate or not through to the other units, as above.
Does anyone have first hand experience of this?
Posted: Thu, 08 Mar 2018, 04:07
by Tejota
Yes. I lost 4 (four) pip4048ms on cluster. Full disaster. I dont know what happened....
Working conditions: 1 pip4048 (master) manufactured August 16 (no heatsink on top) + 3 Axpert 5048 (4kW) (slaves) manufactured Mars 2014 (heatsink on top). Firmware 72.70c on all units. Lead Acid Battery 1500 Ah. At midday global solar production about 9 kW 160A (40+40+40+40 more less) to battery and a little inductives load in AC (2 kW). A little cloud effect.... not important. Suddenly ALL DC breakers of slave units OPEN. Only DC breaker of master closed but all units in fault.
I disconnect everything. Two slaves shorted at battery side. One slave starts at fault 09 and shutdown. Master starts at fault 09 and shutdown.
I only have dissambled one shorted slave: 12 mosfets shorted, 2 mosfets fifty fifty, and 2 mosfets correct. Buck IGBT (2) shorted !!!
No visual destructive effects.
Any explanation of this disaster ?? Mosfets and capacitor were original on failed units.
Pd: Yes I bought an axpert 5048 pf1 64V until I repair failed units if I can.
Posted: Thu, 08 Mar 2018, 06:03
by curasun
Hello guys I'm from Curacao, a small Island in the carribean sea.
I've Learned a lot on this forum.
After a lot of reading,Youtube and other forums. Ive decided to to order the PIP 4048ms Inverter charger. Ive got the 12-2017 model firmware 73.0.
It Arrived yesterday and it is installed and doing its job.
Ive 2kw of panels and a 400ah battery Lead acid connected to it, my only load for now is the AC of my room. 1kw of panel thru another charge controller and 1kw thru the 4048.
2 questions can someone explain to me the setting # 1 and #31 please,
Ive settings # 32 and so on, but cann't find what this mean in manual, please help.
thanks in advance
R.G.Specht
Dutch Carribean Curacao.
Posted: Thu, 08 Mar 2018, 06:11
Hi curasun,
See page 23 of the online manual via the first link in our index post. Also see the link "Weber's table about parameter 1, Output Source Priority", in the index section headed "Parameters (LCD settings)".