Tesla PW2
Damn this guy called Elon Musk. He hit my weak spot. I have this unhealthy addiction to anything battery powered and inverters. When one combined them both, then who am I to resist? Need to remortgage the house for this, hence, my family will live on boiled water and salt from now on (powered by PW2)!
Wheel added so it can fit to a 'vehicle' forum:
My observation to date, can be found here.
Too bad Tesla took the wording out of the older advertisement: "Powerwall provides backup power during utility outages, natural disasters and even the Zombie Apocalypse (you know it's coming).". Since it's pretty much what it is at the current cost.
Wheel added so it can fit to a 'vehicle' forum:
My observation to date, can be found here.
Too bad Tesla took the wording out of the older advertisement: "Powerwall provides backup power during utility outages, natural disasters and even the Zombie Apocalypse (you know it's coming).". Since it's pretty much what it is at the current cost.
-
- Senior Member
- Posts: 810
- Joined: Tue, 02 Dec 2008, 00:15
- Real Name: Michael Dufty
- Location: Perth, Western Australia
- Contact:
Re: Tesla PW2
Is the anti islanding, backup function when the grid goes down built in, or something that had to be installed specifically? Couldn't find much detail of that in their webpage previously.
Roughly how much did it cost installed?
Roughly how much did it cost installed?
-
- Groupie
- Posts: 320
- Joined: Mon, 09 Jun 2014, 16:45
- Real Name: Rusdy
- Location: Australia
- Contact:
Re: Tesla PW2
The battery and the 5kW inverter is definitely built-in to the same enclosure (with the big a$$ Tesla logo on it). The 'Gateway' box, from what the installer told me (and also from Tesla's block diagram) contains a 'switch'. I'm guessing this is a remote controlled switch (controlled by the PW2) as an anti-islanding switch. During installation, I did see a big ass circuit breaker on the 'gateway' box. The gateway box is ugly as.
So that we're on the same page, the gateway box is a separate enclosure and must be installed close to the electricity meter / DB:
It cost me AUD12,100. However, my PW2 is quite a distance from the gateway box (roughly 15 metres). Also, I got charged extra since my house is 3-phase (4 CTs to monitor 3 phases and solar input).
So that we're on the same page, the gateway box is a separate enclosure and must be installed close to the electricity meter / DB:
It cost me AUD12,100. However, my PW2 is quite a distance from the gateway box (roughly 15 metres). Also, I got charged extra since my house is 3-phase (4 CTs to monitor 3 phases and solar input).
-
- Groupie
- Posts: 320
- Joined: Mon, 09 Jun 2014, 16:45
- Real Name: Rusdy
- Location: Australia
- Contact:
Re: Tesla PW2
For those who have PW2, and found the new TBC (Time Base Control) is confusing, I did a wee bit different experiments and concluded that TBC Cost Saving with peak time extension to cover the shoulder is not a bad idea (in order to reduce solar exports, for those with poor FiT).
I also found a quirk that stop the PW2 charging from the grid during off-peak. More details here.
I also found a quirk that stop the PW2 charging from the grid during off-peak. More details here.
- Adverse Effects
- Senior Member
- Posts: 1172
- Joined: Sat, 01 Jan 2011, 03:30
- Real Name: Adverse Effects
- Location: Brisbane
Re: Tesla PW2
you beat me to it been watching him for a year or 2 lolreecho wrote: ↑Sat, 09 Jun 2018, 20:06 Interesting info from a Tesla owner on his new PW2 install..
https://youtu.be/c9jpLItCJws
he lives a not to far from me
If you don't have time to do it right,
When will you have time to do it over
Help those who help themselves first
When will you have time to do it over
Help those who help themselves first
Re: Tesla PW2
Interesting.. Obviously a very savvy guy.Adverse Effects wrote: ↑Sat, 09 Jun 2018, 21:06you beat me to it been watching him for a year or 2 lolreecho wrote: ↑Sat, 09 Jun 2018, 20:06 Interesting info from a Tesla owner on his new PW2 install..
https://youtu.be/c9jpLItCJws
he lives a not to far from me
One question springs to mind though.. (2 actually !) ..
1)..With all the impressive data capture and display (how many monitors ).. Why did he need to hack together a separate LCD etc to show the PW capacity level ?
2)..And , what was the readout on that LCD showing ? ...84.??? What ? Cetainly not kWh (or does he have 7+ PW units ?)
But anyway,.. i thought there was a phone App that gave realtime PW data remotely ?
-
- Noobie
- Posts: 23
- Joined: Wed, 25 Feb 2015, 20:10
- Real Name: Adam Lippiatt
- Location: Perth
Re: Tesla PW2
Hi
Does anyone have current pricing in Perth for the Powerwall 2? Any installer that can be recommended?
I have a quote from over east company but I am starting to worry about the install as they told me that western power is no longer allowing the install of powerwall 2s on single phase properties with any solar already installed.
I got in touch with Western Power and they confirmed it is a 5kVA grid tied inverter limit that is in place. Affects people who already have solar adding a battery and using a hybrid inverter plus their existing grid tied inverter. Not powerwalls.
That they couldn’t tell the difference worries me.
Thanks
Adam
Does anyone have current pricing in Perth for the Powerwall 2? Any installer that can be recommended?
I have a quote from over east company but I am starting to worry about the install as they told me that western power is no longer allowing the install of powerwall 2s on single phase properties with any solar already installed.
I got in touch with Western Power and they confirmed it is a 5kVA grid tied inverter limit that is in place. Affects people who already have solar adding a battery and using a hybrid inverter plus their existing grid tied inverter. Not powerwalls.
That they couldn’t tell the difference worries me.
Thanks
Adam
-
- Senior Member
- Posts: 1952
- Joined: Thu, 30 Sep 2010, 20:11
- Real Name: Terry Covill
- Location: Mannum SA
Re: Tesla PW2
Doesn't the Powerwall have a hybrid inverter built in to it? Do you already have grid tie solar?
T1 Terry
T1 Terry
Green but want to learn
- jonescg
- Senior Member
- Posts: 4721
- Joined: Thu, 21 Jan 2010, 23:05
- Real Name: Chris Jones
- Location: Perth, WA.
- Contact:
Re: Tesla PW2
It's an AC coupled system, so it comes with an inverter built in. Easiest option for retrofits to grid-tied solar.
AEVA National President, WA branch director.
-
- Senior Member
- Posts: 1952
- Joined: Thu, 30 Sep 2010, 20:11
- Real Name: Terry Covill
- Location: Mannum SA
Re: Tesla PW2
So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook
T1 Terry
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook
T1 Terry
Green but want to learn
-
- Senior Member
- Posts: 940
- Joined: Sun, 17 Apr 2011, 02:39
- Real Name: Richard
- Location: Perth WA
- Contact:
Re: Tesla PW2
No...Original grid tie can stay as is.T1 Terry wrote: ↑Thu, 29 Aug 2019, 15:18 So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook
T1 Terry
-
- Senior Member
- Posts: 3183
- Joined: Mon, 26 Nov 2007, 05:39
- Real Name: Matthew Lacey
- Location: Perth, WA
Re: Tesla PW2
Especially if you install it without telling Western Powerreecho wrote: No...Original grid tie can stay as is.
best of luck with the bureaucracy
Matt
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
-
- Senior Member
- Posts: 826
- Joined: Mon, 17 Sep 2018, 16:30
- Real Name: Francisco
- Location: Brisbane, Strathpine
Re: Tesla PW2
Or you could install enough backup and panels to run off grid and tell western power that you are moving and do not want the connection anymore.
It seems it is becoming easier to go off grid. It is just a matter of how much you get for your excess electricity vs how much you pay in connection fees.
It seems it is becoming easier to go off grid. It is just a matter of how much you get for your excess electricity vs how much you pay in connection fees.
-
- Senior Member
- Posts: 513
- Joined: Tue, 05 Jul 2011, 16:32
- Location: Brisbane
Re: Tesla PW2
Just on the idea of going off grid completely.
I have taken notice of those times where you have heavy cloud cover for days on end, or sun showing on and off all day.
Being off grid would be great until you get that scenario. You'd have to accept that possibility and just wing it for as long as it takes for good old sunshine to kick in again. You couldn't live in a household where not everyone understood the significance of being off the grid.
Living in parts of Australia which really do have lots of sunshine and unfortunately a minimum of rain would be a bonus, to this extent.
As the weather becomes more and more unpredictable and we get cloudy days instead of fine or rain, it is a factor.
I have taken notice of those times where you have heavy cloud cover for days on end, or sun showing on and off all day.
Being off grid would be great until you get that scenario. You'd have to accept that possibility and just wing it for as long as it takes for good old sunshine to kick in again. You couldn't live in a household where not everyone understood the significance of being off the grid.
Living in parts of Australia which really do have lots of sunshine and unfortunately a minimum of rain would be a bonus, to this extent.
As the weather becomes more and more unpredictable and we get cloudy days instead of fine or rain, it is a factor.
Re: Tesla PW2
Have played with the idea of using excess sunny days to run a water pump to fill a number of water tanks.and then release water to run water wheels for base loads on cloudy days. 200 wet days year.
- jonescg
- Senior Member
- Posts: 4721
- Joined: Thu, 21 Jan 2010, 23:05
- Real Name: Chris Jones
- Location: Perth, WA.
- Contact:
Re: Tesla PW2
For times like this, a small petrol generator would suffice. It's prudent to have a plan C anyway.
AEVA National President, WA branch director.
- jonescg
- Senior Member
- Posts: 4721
- Joined: Thu, 21 Jan 2010, 23:05
- Real Name: Chris Jones
- Location: Perth, WA.
- Contact:
Re: Tesla PW2
For about 11 years, my folks lived in the bush east of Warwick where we had a solid 400 m of elevation behind the house. The top of the ridge wasn't our land, so it was moot, but as an exercise I worked out how much water, head, pipe and power was needed for a small scale pumped hydro scheme. I think I concluded I'd need about 100,000 litres on top of the hill, and a minimum of 25 kW of daytime solar pumping power to supply 12 hours of 3 kW of base load power. I don't think UPVC was able to restrain that much pressure, but would have been a fun (albeit expensive) exercise.
Assuming 1 litre per second flow and 400 m of head, that's 3.5 kW of power on tap. So for 24 hours you would need to release 86400 litres.
AEVA National President, WA branch director.
Re: Tesla PW2
Throw in 4 ram pumps as well for fun
-
- Senior Member
- Posts: 1952
- Joined: Thu, 30 Sep 2010, 20:11
- Real Name: Terry Covill
- Location: Mannum SA
Re: Tesla PW2
The bother in law does have a mix of solar and hydro to charge his house battery. It is a very old Telecom lead acid battery so it doesn't hold capacity well, so must be recharged daily. He lives on the side of the Huon Valley in Tasmania, about as far south as most would live full time and Tassie is known for its generous rain fall and cloud cover.
His hydro uses a Pelton Wheel, just needs a good flow rather than high pressure, he has 2 permanent springs that feed his supply dam but there is no reason why a constant supply from something like this https://www.ebay.com.au/itm/DC-24V-284W ... 2749.l2649 couldn't be powered from a combo of solar and wind. There is the potential to add as many supply jets as required to get the required torque and jet size to get the required speed while balancing that against water use.
Not quite the idea solution for an urban house off grid system, but great for a country property with a suitable hill near the house.
His hydro uses a Pelton Wheel, just needs a good flow rather than high pressure, he has 2 permanent springs that feed his supply dam but there is no reason why a constant supply from something like this https://www.ebay.com.au/itm/DC-24V-284W ... 2749.l2649 couldn't be powered from a combo of solar and wind. There is the potential to add as many supply jets as required to get the required torque and jet size to get the required speed while balancing that against water use.
Not quite the idea solution for an urban house off grid system, but great for a country property with a suitable hill near the house.
Green but want to learn
-
- Senior Member
- Posts: 826
- Joined: Mon, 17 Sep 2018, 16:30
- Real Name: Francisco
- Location: Brisbane, Strathpine
Re: Tesla PW2
Plan C would be to have two electric cars with 40kwh+ battery each and when supply is too low run off the car battery. When car is getting low you can go to a fast charger and recharge.
If you use say 12kwh/day your car batteries would keep you going for about a week.
If you use say 12kwh/day your car batteries would keep you going for about a week.
-
- Noobie
- Posts: 23
- Joined: Wed, 25 Feb 2015, 20:10
- Real Name: Adam Lippiatt
- Location: Perth
Re: Tesla PW2
Yes, the original grid tied inverter stays as is.reecho wrote: ↑Thu, 29 Aug 2019, 18:44T1 Terry wrote: ↑Thu, 29 Aug 2019, 15:18 So the original grid tie inverter would have to be removed to be able to fit the Powerwall? Here in South Australia, as soon as you touch anything to do with a grid tie system, the whole thing has to be renegotiated and generally results in a much smaller feed in tariff.
The 6kW solar and 15.5kWh battery pack we installed in Crystal Brook had to be totally separate from any connection to the grid what so ever or they would reduce his feed in tariff for the existing grid tie solar.
Now the only parts of his house on the grid is 4 power points in the kitchen and the 3 phase ducted air conditioning. Now he only knows the grid went down if visitors tell him or dinner seems to be taking a long time to cook
T1 Terry
No...Original grid tie can stay as is.
The issue is when you install a hybrid inverter with an existing grid tied inverter. Western Power will count both for their 5kVA limit, even if you just propose using the battery inverter component.
In any event, installing a Powerwall which only has a battery inverter does not add towards the five kVA limit.
The downside is the power wall is the more expensive option (at least initially).
-
- Senior Member
- Posts: 1952
- Joined: Thu, 30 Sep 2010, 20:11
- Real Name: Terry Covill
- Location: Mannum SA
Re: Tesla PW2
Then you need the inverter that can handle the electric vehicle battery voltage.francisco.shi wrote: ↑Sat, 31 Aug 2019, 12:13 Plan C would be to have two electric cars with 40kwh+ battery each and when supply is too low run off the car battery. When car is getting low you can go to a fast charger and recharge.
If you use say 12kwh/day your car batteries would keep you going for about a week.
That raises an interesting thought. The inverter I'm looking at to use on a proposed off grid system has a solar feed in voltage max of 450vdc and between 120vdc and 430vdc the MPPT controller part can handle. If the electric vehicle battery was between these 2 figures, 120vdc and 430vdc, could the EV battery be connected to the solar input of the inverter to act as a supply?
T1 Terry
Green but want to learn
-
- Senior Member
- Posts: 3183
- Joined: Mon, 26 Nov 2007, 05:39
- Real Name: Matthew Lacey
- Location: Perth, WA
Re: Tesla PW2
Yes that works (I do that for capacity testing large packs)T1 Terry wrote: ↑Sat, 31 Aug 2019, 14:58
Then you need the inverter that can handle the electric vehicle battery voltage.
That raises an interesting thought. The inverter I'm looking at to use on a proposed off grid system has a solar feed in voltage max of 450vdc and between 120vdc and 430vdc the MPPT controller part can handle. If the electric vehicle battery was between these 2 figures, 120vdc and 430vdc, could the EV battery be connected to the solar input of the inverter to act as a supply?
The inverter will run at full power though until you either disconnect it, or the voltage goes outside it's operating window
Matt
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
2023 BYD Atto 3 - 21k km
2017 Renault zoe - 147'000km
2012 Leaf - 101'000km - soon to be trialing a booster battery
2007 Vectrix - 197'000km (retired)
2007 Vectrix - 50k km
-
- Senior Member
- Posts: 826
- Joined: Mon, 17 Sep 2018, 16:30
- Real Name: Francisco
- Location: Brisbane, Strathpine
Re: Tesla PW2
I have been thinking about how to do this. As you said most solar panel strings would be able to feed the car battery directly. And most solar inverters I assume would have a 400 or so volt bus. So it may be as simple as just connecting the car battery to the internal bus and reprogramming the inverter.
This could potentially fix the duck curve produced by solar without having to spend money in storage. As we get more electric cars they can be used as domestic energy storage.
This could potentially fix the duck curve produced by solar without having to spend money in storage. As we get more electric cars they can be used as domestic energy storage.