Yesterday, 21:10
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

data wrote:
Yesterday, 20:58
We have a couple of 2424MSD here. Reason for swapping out the serial board is, that it is crap.
Oh. My misunderstanding then. Sorry.

I thought you could get the serial boards, and other spares, from MPPSolar.
by coulomb
Yesterday, 20:04
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

where can I order a serial/RS232 module for the inverter? We mention Jaycar for the serial to RS-232 board. However, see below. Mine has the USB-only board... Ah. As far as I know, no models that have the USB-only board can use the firmware (factory or patched) found on this site. I don't understan...
by coulomb
Fri, 18 May 2018, 19:47
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

any idea how can i stop this ? or, where to start ? If you have the ability to inject commands to the PIP, and since you are using patched firmware, I'd try this pair of commands: MNCHGC0500 <CRC><CR> MNCHGC0499 <CRC><CR> This sets the dynamic charge current to zero, then sets it back to the EEPROM...
by coulomb
Fri, 18 May 2018, 17:10
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Hi , and thank you again for all the help , I have disconnected the panels , but the problem remains, Ok. So that seems to rule out leakage across your PV switch. and in bypass mode and what i have observed is that i have 1 amp drain from batteries no matter what( reported by the inverter himself ,...
by coulomb
Fri, 18 May 2018, 06:33
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

And measured with a multimeter , even with the pv switch off , i have that 46v there , By "there", do you mean at the PV input terminals? Is it possible that this is leakage across your PV switch? For example, can you ever see this 46 V at night? so , somehow is taking dc current from another place...
by coulomb
Thu, 17 May 2018, 07:10
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Yes, I have a Pip4048ms .... the problem remains even when the battery is removed. the relays seem to work well in the mppt card but not released under the 60v photovoltaic input Hi , did you solve the problem? I have the same issue , He worked great , until now .Thank you ! If you mean that the re...
by coulomb
Fri, 11 May 2018, 21:24
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

When you say it uses the battery current at a certain voltage, do you mean when the inverter is on it can guess the SOC because of the voltage at that load? No, it's all based on total battery current. What happens when the inverter isn't on, what current is it using then? Sorry, I forgot to mentio...
by coulomb
Fri, 11 May 2018, 21:12
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Coulomb, do you know if your custom firmware would work on a 'POWER MPS-5K, Model: MPS 5K-48VDC'. https://rover.ebay.com/rover/0/0/0?mpre=https%3A%2F%2Fwww.ebay.com.au%2Fulk%2Fitm%2F122360096080 The above link goes to a 24 V model for me. Looking at the 48 V model specifications, I'd say that these...
by coulomb
Fri, 11 May 2018, 07:58
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Coulomb, do you know if your custom firmware would work on a 'POWER MPS-5K, Model: MPS 5K-48VDC'. It's difficult to know. These inverters are identical to the Axpert. As long as they are genuinely Voltronic Power made, it should work. Do you have a link to the Ebay advertisement? I could not find it.
by coulomb
Thu, 10 May 2018, 20:35
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Edit: Please trim your quotes to just what is needed to establish context. For two posts, you quoted my entire post, including quotes from your questions, when only a sentence or two was needed. It makes it easier to other readers to find information that way. Thanks. ... when in bulk mode it goes u...
by coulomb
Wed, 09 May 2018, 16:55
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

so in "bulk" mode you will see a rise to 56v and then it is in absorb. Yes. I guess the thing which seems weird to me is aren't the batteries full at ~52v for AGM . Battery terminal voltages are a bit weird. 52 V (13.0 V per 12 V module, or 2.167 V per 2 V cell) is indeed a good 100% SOC voltage, b...
by coulomb
Wed, 09 May 2018, 06:18
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

but I saw in the last firmware update that I can set maximum charging from zero, is it not true? Sigh. I'd forgotten that patch; it's one of the earlier ones. So yes, you could use that instead of turning the machine off. I don't know if the firmware will "idle" some inverters when more paralleled ...
by coulomb
Tue, 08 May 2018, 18:39
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

But I have only 40Ah remaining cells Ah. So that's why you only want one unit charging. I believe that even with no solar connected, you still can't set the maximum total charge (setting) to less than 10 A, so they will still contribute towards the total maximum charge current for the system. This ...
by coulomb
Tue, 08 May 2018, 18:16
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

I am on 73.00b though. I have 8 x 12v 120ah batteries. The led was flashing. Ah, I failed to remember that you were on 73.00b. Flashing LED, so you are in bulk or absorb. All good. I thought it would attempt to hold 56v whilst in bulk/absorb. Sure, it will have 56.4 V as its setpoint. It can't get ...
by coulomb
Tue, 08 May 2018, 14:49
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Is there a way to disable battery charging for 4 pcs from 5 parallel connected inverters? Sure, don't connect solar to the four, and they won't charge. I don't know why you'd want to do this, however; why not spread the charging load? Charging current limits are separate for paralleled inverters. Y...
by coulomb
Tue, 08 May 2018, 11:26
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Is it normal for the PIP to not have a float or bulk/absorb voltage ? No. It should be aiming for either float or absorb voltage, depending on the mode. Check the charge LED (middle, green LED) to see if it is not charging at all (dark), bulk/absorb (flashing), or at float (solid green). Shouldn't ...
by coulomb
Sat, 05 May 2018, 22:09
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

As far as I can see, this matches the "Charge termination conditions" you mention in your post. If using a timed absorb period rather than automatic absorb terminated by charge current I would prefer it if the absorb period was not terminated by charge current but by time alone. This is the origina...
by coulomb
Wed, 02 May 2018, 07:36
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

Also worth noting. Both HRC fuses had blown. Has anyone had this experience? I'm assuming the pip developed a short?? It's not uncommon that when a PIP goes faulty, that it blows its MOSFETs, which fail shorted and present a short circuit across the battery. Surprisingly, this rarely results in bat...
by coulomb
Tue, 01 May 2018, 06:54
Forum: Technical and conversion discussion
Topic: innovation
Replies: 17
Views: 299

Re: innovation

it will still use solar but there is something else im going to do Solar insolation is about 1 kW/m² peak, and solar panels are roughly 20% efficient, so 200 W/m². So perhaps 400 W on a typical vehicle. Compare that with typically 20,000 W for highway cruising, 10 kW for low speed level driving, an...
by coulomb
Mon, 30 Apr 2018, 12:08
Forum: Technical and conversion discussion
Topic: innovation
Replies: 17
Views: 299

Re: innovation

In this forum, we obey the laws of physics! I'm afraid that "self charging" is going to provoke comments like this. Do you perhaps mean wireless charging? That's at least a little more believable, though with plenty of practical issues. If you mean charging via solar power, a little arithmetic revea...
by coulomb
Mon, 30 Apr 2018, 06:51
Forum: Batteries, charging, management and monitoring
Topic: Arvio 3.5kWh drop-in-battery-replacement supercapacitor on sale
Replies: 263
Views: 9982

Re: Arvio 3.5kWh drop-in-battery-replacement supercapacitor on sale

Yeh cause having a range up to 85deg and running at 85deg for prolonged lengths is equivalent. :lol: Capacitors do have a rated lifetime at the maximum rated temperature. The best electrolytic capacitors, which I'm more familiar with, have for example a life of 10,000 hours at 105°C. That's all 10,...
by coulomb
Sun, 29 Apr 2018, 17:40
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

The SCC firmware is showing as 00000.00 and PV volts=0 and PV watts=0 during the day. It's like the SCC is dead. Under these conditions, I don't think you can update the SCC firmware. I assume you've checked for ≥ 60 VDC at the PV input with a multimeter? The msdos does not recognise the command re...
by coulomb
Sat, 28 Apr 2018, 15:46
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

My inverter just stopped working. It shows error 90, no error 90 is included in the manual. Does anybody know what error 90 means? It's not documented anywhere, so no one knows for sure. You can read my wild speculation here: http://powerforum.co.za/topic/1865-axpert-error-code-90/ Unfortunately, i...
by coulomb
Thu, 26 Apr 2018, 20:34
Forum: Technical and conversion discussion
Topic: Prelude conversion project - some questions
Replies: 38
Views: 1211

Re: Prelude conversion project - some questions

Isn't this a comment error? :oops:

pinMode(2, OUTPUT); // declare pin 5 as an output (AC compressor)

Later comments talk about pin 2.

Yes, I'm a pedant. :geek:
by coulomb
Mon, 23 Apr 2018, 10:05
Forum: The Lounge
Topic: PIP-4048MS inverter
Replies: 2195
Views: 222982

Re: PIP-4048MS inverter

... I have changed the defected parts of Main board Mosfets and IGBTs But I think there is problem in Control Board Have you find any problem in your previous projects ? No, I can't recall any problems with a control board, though I faintly remember attempting to trace a few parts of one once. The ...