Search found 5 matches

by jdavies1994
Tue, 19 Feb 2019, 05:29
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2725
Views: 442501

Re: PIP-4048MS and PIP-5048MS inverters

swagner2018 wrote:
Tue, 19 Feb 2019, 01:27
Today I've tried to update the firmware but I get always in the ReflashTool "Can not open serial port"
Have you made sure watch power is definitely closed and the com port is open.

[ Edited Coulomb: trimmed quote ]
by jdavies1994
Sun, 17 Feb 2019, 18:14
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2725
Views: 442501

Re: PIP-4048MS and PIP-5048MS inverters

Good work on that clone post coulomb. I have 8 X 16mm (2 for positive and 2 for negative on each inverter and only 1.5 meters long) The voltage is fine until I boil the kettle (around 50a) and I get around 4/5v drop across the pack. Probably says more about the batteries. They were sold as deep cycl...
by jdavies1994
Sun, 17 Feb 2019, 07:42
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2725
Views: 442501

Re: PIP-4048MS and PIP-5048MS inverters

This is the ones I bought but I got shipped 80a versions. The certificates all said voltronic when I bought them :| 898.83 6%OFF | MPPT Solar Inverter 60A off Grid Solar System 2pcs Parallel Pure Sine Wave Power Battery Charger Inversor Parallel Kit Card Free https://s.click.aliexpress.com/e/chYv878...
by jdavies1994
Sat, 16 Feb 2019, 21:55
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2725
Views: 442501

Re: PIP-4048MS and PIP-5048MS inverters

Tried forcing closed watch power in task manager so the com port is definitely not in use. I don't think that actually guarantees that the COM port isn't in use, since the forced closing may well bypass the cleanup code that closes the port. However, it sounds like you've been quite thorough in all...
by jdavies1994
Sat, 16 Feb 2019, 20:29
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2725
Views: 442501

Re: PIP-4048MS and PIP-5048MS inverters

Hello everyone, I'm having a little trouble updating my inverter. Everytime I click update the Inverter locks up followed by connection failed on my computer. I have tried setting to com 1 (reads ok in watch power). Tried forcing closed watch power in task manager so the com port is definitely not i...