Search found 27 matches

by daimyo
Wed, 18 Mar 2020, 03:16
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

So my observation is that temperature is not displayed properly (max temperature on inverter). I assume that this is happening during the day while the Solar Charge Controller is running. It could be that the SCC sensor is on the MOSFET heatsink, and not on the heatsink on top, which I believe is f...
by daimyo
Sun, 15 Mar 2020, 18:01
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

What temperature is measured and than displayed on my Pips 4048MS with your latest "e" FW? It's the highest of 3 or 4 temperatures: The battery-side MOSFET heatsink The inverter proper (IGBT) heatsink The transformer temperature (there is a bead sensor near the transformer) The SCC heatsink tempera...
by daimyo
Thu, 12 Mar 2020, 22:47
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Hi guys, What temperature is measured and than displayed on my Pips 4048MS with your latest "e" FW? It shows about 31 and upper heatsink is for sure about 50 degrees Celsius. Other question is: Is it possible to get all display menu items on both left and right side od display? That would be most us...
by daimyo
Fri, 14 Feb 2020, 00:15
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Ebay seller said that V2 model is EOL and new model is: https://www.ebay.com/itm/163192198388 ? But the one shown in the Ebay advertisement is a V2. Perhaps he/you meant that the V are now at end-of-life, and the V2 are replacing them. But the V2 are 450 V max MPPT models, so you'd need to add insu...
by daimyo
Thu, 13 Feb 2020, 14:00
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

coulomb wrote:
Mon, 10 Feb 2020, 17:23
I did not find 4048V model on ebay? Do you have some link to it?
https://www.mppsolar.com/v3/hybrid-v-series/
Ebay seller said that V2 model is EOL and new model is:

https://www.ebay.com/itm/163192198388
by daimyo
Wed, 12 Feb 2020, 19:00
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Could it be connected in parallel with my 3 existing 4048MS? No. I did not find 4048V model on ebay? Do you have some link to it? https://www.mppsolar.com/v3/hybrid-v-series/ The V series are hybrids, not off-grid models... Thank You... things are now much more clearer. :) [ Edited Coulomb: trimmed...
by daimyo
Mon, 10 Feb 2020, 15:18
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

solamahn wrote:
Sat, 08 Feb 2020, 13:41
4048V can export to grid
Hi,

Could it be connected in parallel with my 3 existing 4048MS?

I did not find 4048V model on ebay? Do you have some link to it?

Could You please give some more info?

Do you know if 5048MK can export to grid?

Thank You and best regards

T
by daimyo
Wed, 05 Feb 2020, 18:46
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Does anyone know is it possible to "return" excess power, when batteries are full, to grid (power company) with PIPs or I have to buy new 10kW grid inverter to do that? My understanding is that the models that can operate without a battery (so that excludes yours) can in some modes push power from ...
by daimyo
Wed, 05 Feb 2020, 18:21
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Hi,

I have 3xPIP-4048MS with 5400W PV and I am adding 5500W more...

Does anyone know is it possible to "return" excess power, when batteries are full, to grid (power company) with PIPs or I have to buy new 10kW grid inverter to do that?

All suggestions are welcome :)

Thank You.
by daimyo
Wed, 29 Jan 2020, 22:39
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

solamahn wrote:
Tue, 28 Jan 2020, 09:22
New type scc pcb USD59
From where do you get spare parts? :roll:

Thank You.
by daimyo
Wed, 29 Jan 2020, 22:38
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

What is the difference between old and new ssc board? Basically, the new board is much longer, the new SCC heatsink is better positioned in front of the fans, and the PV terminal block connects to the SCC PCB via a pair of metal bars attached to the PCB. Old board (sorry for the poor photo, all I c...
by daimyo
Tue, 28 Jan 2020, 05:55
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP-4048MS and PIP-5048MS inverters

New type scc boards can be fitted to old type 4048ms with the big black heatsink. Leave the heatsink but remove the old scc pcb. Mount the new type scc pcb between the 2 main board heatsinks sand connect to the 2 inductors which remain on the big black heatsink Hi, What is the difference between ol...
by daimyo
Sun, 26 Jan 2020, 14:53
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

Does anyone knows how to resolder original fan connector to Arctic fan? This post may be helpful. Available from the index. Edit: but take note of this post , where Weber put back the original fans due to intermittent fan locked warnings. Also available from the index in the first post of this topi...
by daimyo
Sun, 26 Jan 2020, 06:21
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Hi,

Today have finally made some time to update my PIP firmware from 52.30 to 73.00e on my 3 inverters. ;)

Everything works excellent for now.

Thank you guys.

Best regards

:D
by daimyo
Sun, 26 Jan 2020, 06:02
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

Its shown in video, arctic f8 pwm, this are very quiet. Until now has only two times occurred the fan lock error. And thats long time ago. If you can live with that is fine, you have been warned. Don't forget to reorient the fan to blow upwards, the inverter is much cooler. Hi again, :D Does anyone...
by daimyo
Fri, 08 Feb 2019, 06:20
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

A story about fans> I have changed all mine so they push air up I have also added two more 120mm fans to the top vents on the inverter drawing air out. I have used a 12v version of this temperature controller to operate them you could use a 240v version and my friend has aswell https://www.ebay.com...
by daimyo
Fri, 01 Feb 2019, 08:14
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

Its shown in video, arctic f8 pwm, this are very quiet. Until now has only two times occurred the fan lock error. And thats long time ago. If you can live with that is fine, you have been warned. Don't forget to reorient the fan to blow upwards, the inverter is much cooler. Thank You... have found ...
by daimyo
Wed, 30 Jan 2019, 14:49
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

catalincre wrote:
Tue, 29 Jan 2019, 00:21
@daimyo can you look on Youtube for that, I have posted a video. Is very easy with the right tool and skills (I'm an obstetrician)....... No I'm not, is a joke. But you get the idea?
Forget to ask... what fan did you use as replacement?

Thank You very much and best regards
by daimyo
Wed, 30 Jan 2019, 14:47
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

Thank You guys so much for answers!

Will try to figure something out. :D

Is there any web place from where to buy original fans? Ebay or...?

Thank you and best regards
by daimyo
Mon, 28 Jan 2019, 05:19
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP inverter repairs and hardware modifications
Replies: 450
Views: 29200

Re: PIP inverter repairs and hardware modifications

Hi guys.

Oldest of 3 inverters has error 01... fan not working.

What is the simpliest way to replace defective fan?

What fan do i need, what connector on fan?

Do I need to unmount inverter from the wall to replace it?

Thank you and best regards
by daimyo
Wed, 02 Jan 2019, 14:55
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

All clear now. ;)

Thank You so much for clarification!

Best regards

Teo
by daimyo
Wed, 02 Jan 2019, 00:46
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

First, Happy New Year to everyone! :) In this year I have few questions for experts on this forum: 1. Currently my inverters are on 1.24 SCC firmware, so do I need to upgrade SCC firmware, and if Yes what will I benefit from it? 2. In Your current 73.00e firmware, under menu [12], can I adjust volta...
by daimyo
Thu, 20 Dec 2018, 23:22
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Hi @daimyo. I'm sorry that the Dynamic Load Control feature of our recent patched firmwares does not do any of those things. It only provides the serial commands that allow such things to be done by a computer connected to any one of the inverters. You would need to write the software yourself. I w...
by daimyo
Wed, 19 Dec 2018, 20:29
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

@Coulomb or @Weber Could You guys please explain how Dynamic load works in real life, lets say on example on my 3 paralel inverters? When load is low, does only one inverter takes all load on himself and other two goes to stanby? What will happend during the night when I turn manual switch to grid s...
by daimyo
Wed, 19 Dec 2018, 20:22
Forum: Renewable Energy and Storage (Non-EV)
Topic: PIP-4048MS and PIP-5048MS inverters
Replies: 2572
Views: 539483

Re: PIP-4048MS and PIP-5048MS inverters

Hi daimyo . Thanks for your kind words. So maybe the best way is to wait some more time and then to install 73.00e FW? Yes. We will probably bump 73.00e from beta to release early in the new year if no one reports any problems. Do I need to turn OFF other two inverters when doing FW upgrade on one?...